Can anybody please help me as im one who does try to do the job correctly, but im unable to find the correct answers anywhere.

The issue is this, i have tested a number of Smart board Projectors and the readings are example of 4.

1 - 3.4mA
2 - 3.6mA
3 - 3.2mA
4 - 3.6mA

very close to the common 3.5mA, i would fail two of these projectors, but im thinking there is a get out clause maybe, like its about 5mA or upto max 10mA for projector or maybe rely on RCD protection been hard wired as well

number 2 is plugged in to a socket above the ceiling and 4 is hard wired to a Spur.

Could you direct me to some figures not say so please as gaffas need answers not jack said hehe. :)

Thanks guys for you time here..
 
you can't fail them. all this type of equipmwnt has a small leakage. just like computers. that's why you should only wire a limited number to each RCD/RCBO.
 
Well I can if I dont get the right answer to be honest, as testing the projector as an item comes in at 3.6mA which is a fail for an appliance, can you explain your answer better telectrix.

I know about Ring circuits and making clean earth to help etc. RCD ratio(mA stuff lol) for circuits but im looking how not to fail the projectors as an item doing PAT testing..
 
Tels point is you cant have to many items that have a leakage to earth i.e projectors and computers on 1 circuit as the accumulative leakage could take it over the 30 m/a threshold
 
Well I can if I dont get the right answer to be honest, as testing the projector as an item comes in at 3.6mA which is a fail for an appliance, can you explain your answer better telectrix.

I know about Ring circuits and making clean earth to help etc. RCD ratio(mA stuff lol) for circuits but im looking how not to fail the projectors as an item doing PAT testing..

Have you read the BGB Reg 543.7.1.101? Have you tried using an earth leakage clamp meter on the equipment you are testing? your PA Tester may be giving you a duff reading
 
How old are these projectors???
Surely all 4 of them are not up the ****ter !!!
I know you said you would fail 2 of them but the others are pretty much the same.
I wouldnt mind betting if you tested them several times you would get different readings and the other 2 would possibly fail aswell.
Anyway pop a pass sticker on and go to sleep !!!:sifone:
 
If it's over 3.5 ma and below 10ma then it should be on it's own circuit
 

Reply to Smart Board Projectors in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K
Hi all. Im looking for some help regards a massive earth leakage issue in a new i installation Its a little more complicated than this but its...
Replies
19
Views
3K
Hello i've recently just had a re wire done on a three bed semi house, Ive noticed a few things im not 100 percent on ive spoken to the firm that...
Replies
24
Views
5K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
J
Hi all, first of all sorry if this thread is not in the correct section...wasn't sure? Ok so basically its not a problem, just wanted to hear...
Replies
49
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top