HI SPARKYS
JUST A QUICK BIT OF ADVICE REQUIRED.
HAVE RECENTLY BEEN TO PRICE A DB CHANGE OF THE DUAL SPLIT LOAD VARIETY.and noticed the instal has a dedicated smoke detection circuit .Now i have also noticed that this circuit is buried in plaster (through a safe zone) and in fact all circuits are buried in plaster as the feeds drop down the wall from ceiling to db level. In no way could I claim that cables are 50 mm back from surface or would be in earthed steel containment
Now due to the circumstances I feel obliged to put smoke detectors on rcd protective device but realize safety services are not required to have additional protection.
Would it be better to put smokes on a rcbo as cables are not 50mm back
Or would it be right to leave circuit without additional protection.
Just for the record I fully believe in the use of 30ma rcd/rcbo and have done for the last 25 years or so as as I believe electrical safety takes precedent over nuisance. I also realize that sometimes incorrect selection of rcds can cause problems to some equipment including fridges and computers etc, and grouping circuits protected by rcds can have a negative impact with some equipment .
So if I put circuit on rcbo and in the future an earth fault was to occur the device was to trip indicating earth fault wouldn't that be better than if left unprotected and the same fault was to occur the protective device may not trip and potentially dangerous leakage currents may be present but smoke detectors still function, whats the point a safety service that can kill you.
I think in this case circuit should be rcbo protected but I have been wrong before.
Anyway sparks what is right db config or if any one wants to get it off their chest what should it be?:shocked:
JUST A QUICK BIT OF ADVICE REQUIRED.
HAVE RECENTLY BEEN TO PRICE A DB CHANGE OF THE DUAL SPLIT LOAD VARIETY.and noticed the instal has a dedicated smoke detection circuit .Now i have also noticed that this circuit is buried in plaster (through a safe zone) and in fact all circuits are buried in plaster as the feeds drop down the wall from ceiling to db level. In no way could I claim that cables are 50 mm back from surface or would be in earthed steel containment
Now due to the circumstances I feel obliged to put smoke detectors on rcd protective device but realize safety services are not required to have additional protection.
Would it be better to put smokes on a rcbo as cables are not 50mm back
Or would it be right to leave circuit without additional protection.
Just for the record I fully believe in the use of 30ma rcd/rcbo and have done for the last 25 years or so as as I believe electrical safety takes precedent over nuisance. I also realize that sometimes incorrect selection of rcds can cause problems to some equipment including fridges and computers etc, and grouping circuits protected by rcds can have a negative impact with some equipment .
So if I put circuit on rcbo and in the future an earth fault was to occur the device was to trip indicating earth fault wouldn't that be better than if left unprotected and the same fault was to occur the protective device may not trip and potentially dangerous leakage currents may be present but smoke detectors still function, whats the point a safety service that can kill you.
I think in this case circuit should be rcbo protected but I have been wrong before.
Anyway sparks what is right db config or if any one wants to get it off their chest what should it be?:shocked: