Discuss Socket has stopped working in the DIY Electrical Advice area at ElectriciansForums.net

lavanic

DIY
Reaction score
7
A single switched 13 amp socket that my extractor fan is plugged into has stopped working after 10 years. The fan itself works when plugged into another socket. Today I replaced the switched socket like-for-like, but the outlet still does not provide power to anything plugged into it.

As far as I know the outlet does not have its own fuse on the consumer unit, and besides all switches on the unit are "on", and no other sockets, switches or spurs in my home have any issue. The extractor fan's outlet just stopped working a couple of weeks ago.

What could be the problem, could it be something between the consumer unit and the outlet? All wiring was replaced 10 years ago during a house refurbishment.
 
Apologies for not replying sooner… completely missed the thread!

How many cables are behind the socket? If just one set of one live, one neutral, one earth then the cable may come from another nearby socket as a spur off the main circuit, and that is where you may find a loose cable.

Fan works if using another socket, so not the plug fuse.
 
Apologies from me as well. I saw the thread when I was in a hurry, intended to reply later, and completely forgot.
Why is the fan plugged into a socket, rather than being 'wired in'?
Is the socket provided especially for the fan?
I'm wondering if the socket is similar to one that you may find in a loft for a TV aerial amp, where it may not be wired to supply a full 13A, and may be fed from a fused connection unit somewhere.
I once spent several hours chasing down something similar, before I discovered a switched FCU behind some storage racks in the garage, where the switch had been knocked off by someone pushing something back on the shelf.
 
Apologies for not replying sooner… completely missed the thread!

How many cables are behind the socket? If just one set of one live, one neutral, one earth then the cable may come from another nearby socket as a spur off the main circuit, and that is where you may find a loose cable.

Fan works if using another socket, so not the plug fuse.
Hello - thank you for the reply - there is one set of cables behind the socket. Interestingly the cable seems to come out of the wall behind the cupboard in which the extractor sits. I will attach photos below.
 
Apologies from me as well. I saw the thread when I was in a hurry, intended to reply later, and completely forgot.
Why is the fan plugged into a socket, rather than being 'wired in'?
Is the socket provided especially for the fan?
I'm wondering if the socket is similar to one that you may find in a loft for a TV aerial amp, where it may not be wired to supply a full 13A, and may be fed from a fused connection unit somewhere.
I once spent several hours chasing down something similar, before I discovered a switched FCU behind some storage racks in the garage, where the switch had been knocked off by someone pushing something back on the shelf.
Hello, thank you for your comments - I do not know why the fan is plugged rather than wired, it was done by an electrician 10 years ago and has worked without issue till now. Kindly take a look at the photos that I will attach below. It seems just to be a standard 13amp socket.
 
Dear all, please see attached photos of i) open socket (fairly standard?) and ii) the cable that supplies power, which just emanates from the wall behind the unit.

20220517_131442.jpg20220516_105103.jpg
 
You definitely need to find out where that socket is fed from.
 
A bit more information, from looking around above the kitchen cabinets:

There are four cables in total that come out of the wall, from three locations.

  • One cable goes into a junction box that then powers the under-cabinet lights (pictured)
  • One cable goes directly into the socket (as pictured above).
  • Two cables go into another junction box, which then powers other under-cabinet lights. (Also pictured - seems a bit weird to have two cables for that one, given the other under-cabinet lights only have a single power cable? Maybe one is a cable "in", the other is a cable "out" elsewhere, but if so it goes back into the wall).
All other sockets and switches in the kitchen are working - I tested them all with a lamp. The fridge and freezer remain working, the switch for the oven is in the back of a cupboard and is also working. As a reminder, all switches in the consumer unit are "On", and there is no failure in power anywhere else in the house.

I checked the outside wall, there are no cables there - so the cables are all in the plaster.

Any more information that may be helpful, let me know!
 

Attachments

  • 20220520_143036.jpg
    258.8 KB · Views: 5
  • 20220520_144945.jpg
    293.4 KB · Views: 5
You definitely need to find out where that socket is fed from.
This is very likely to be where the problem lies.
It could be in a hidden junction box, or spured from one of the other kitchen sockets.
 
  • Like
Reactions: DPG
I think you need soneone on site.

Having said that, a cable detector may help find where the cable is routed from
 

Reply to Socket has stopped working in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I plugged a drill press directly into a GFCI outlet in the garage. Something blew up by the drill press switch. Since then the GFCI outlet LED...
Replies
1
Views
802
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
541
Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
628
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
735
Hi I have a Corby 7700 trouser press it is a 220w model, 3 years 10 month old. On Friday it stopped working, so I took it to the garage ready...
Replies
1
Views
723

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock