G

Gra426

Hi,

I have a question about socket positions that hopefully somebody could clear up for me. I am planning a kitchen rewire and looking at suitable accessory positions. I am aware that in most instances sockets are positioned a minimum of 300mm from the corner of the room. However I have something in my head that this reg is associated to habited rooms and kitchens may be exempt.

If anyone could clear it up for me it would be much appreciated.

Cheers

Gra.
 
dunno where you got that from. 300mm from sink and hob is a recommendation.
 
I've got a feeling (don't know where from) that the 300 mm is a recommedation, so that you're not tempted to put a back box in the safe zone, in the corner of a room!
 
Yeah that's what I thought Murdoch. However if it's just a recommendation I might try to nick 50 mm just to tidy things up, but naturally will avoid the permitted zones.
 
I've got a feeling (don't know where from) that the 300 mm is a recommedation, so that you're not tempted to put a back box in the safe zone, in the corner of a room!
so what about when you do a drop to a FCU then down to an appliance socket?. that's accessories in a safe zone.
 
i include the drainer as otherwise numpty, lazy housewife will then put kettle on drainer.
 
It includes the drainer - 300mm from the sink or drainer.
There's a minimum height from the work surfaces as well - 150mm off the top of my head.
 
What I meant was if you are adding sockets into a room you should avoid the corners as these are deemed safe zones and another sparky could have run cables there.

I wasn't ignoring the "safe" zone created by an accessory!

Does this help?
 
know what you mean, murdoch, but as professional electricians, we should be aware that there may be cables there. that is unless we are part p kitchen fitters!
 
The top 150mm of the room is also a safe zone; if we weren't allowed to run cables through safe zones that would make running switch drops a little tricky.
 
think the concern is more about some hairy-arsed spark with a sds chisel chopping out for a back box where cables might be lurking.
 
I think it's the same kind of argument - someone may have thought it was a good idea to run a cable around the top of the room because 'it's a safe zone so that means it's fine'.
 

Reply to Socket positions in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
714
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
503
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
874
A rose in my 1970s kitchen ceiling became loose (one fixing screw had been inserted right on the edge of the hole in the ceiling) and when I...
Replies
3
Views
794
Hi All, This might be a bit of an odd question, I would really appreciate your thoughts. I am trying to up-date my mum's home, before putting it...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock