Hello
I'm looking at adding more sockets to a bedroom, I notice the existing single socket has to cables running into it, would it be ok to add twin sockets to the end of each cable or do i need to add another bit of cable to complete the existing circuit?

Thanks for any advice
 
I notice the existing single socket has to cables running into it
Just to check, do you mean two cables?

If there are two cables, then it is likely that the original socket is on a ring final circuit. But you would need to test if this is the case. you'll need a multimeter that can test resistance and mains voltage. Do you have one?

As it is a ring, it is best to add the new sockets and unclude them as part of the ring.
You can add a socket to a ring as an addition (known as a spur) but you can only have one spur. it is not permitted to have a spur from a spur.
 
Just to check, do you mean two cables?

If there are two cables, then it is likely that the original socket is on a ring final circuit. But you would need to test if this is the case. you'll need a multimeter that can test resistance and mains voltage. Do you have one?

As it is a ring, it is best to add the new sockets and unclude them as part of the ring.
You can add a socket to a ring as an addition (known as a spur) but you can only have one spur. it is not permitted to have a spur from a spur.
You can if you first fit a fused spur unit and then as many sockets as you want within reason Appenx15 BS7671
 
best to employ the services of a local sparks. that way the alteration will be to current regulations, tested for safety, and a certificate provided. this could be critical if you came to sell the house.
 
Thanks for all your replies,
Yes two twin and earth cables going into a single socket, It's on an RCD board, haven't attempted it just yet, I do have a multimeter so will check what reading the circuit gives, but I was going to re-wire it as I found it, with an additional cable connecting the two sockets through two junction boxes to create the ring. I've done sockets before without issue, but not seen one on a ring before, so wanted to know the best way to do it. What resistance reading should I be looking for, 0.3 - 0.4?
 
I've done sockets before without issue, but not seen one on a ring before, so wanted to know the best way to do it.

This sounds like an interesting comment. So what where the other circuits where you added extra sockets? How many wired did they have? What size cable?
 
I did them with a qualified electrician, he took me though it, we added fused spurs, it was a few years back in different house, 2.5mm twin earth, I will be consulting an electrician, I'd just like to understand what will be required
 
I've done sockets before without issue, but not seen one on a ring before, so wanted to know the best way to do it. What resistance reading should I be looking for, 0.3 - 0.4?
Well, if they worked, you won't have had any issues......will you?....
 
Thanks for all your replies,
Yes two twin and earth cables going into a single socket, It's on an RCD board, haven't attempted it just yet, I do have a multimeter so will check what reading the circuit gives, but I was going to re-wire it as I found it, with an additional cable connecting the two sockets through two junction boxes to create the ring. I've done sockets before without issue, but not seen one on a ring before, so wanted to know the best way to do it. What resistance reading should I be looking for, 0.3 - 0.4?
Frank with respect you shouldn't be attempting this work, as you obviously have very little knowledge of how to do this type of work, neither do you, by the sounds of it have the corect sort of test gear, do your self a favour and employ an Electrician to do these alterations for you.
 
Just to check, do you mean two cables?

If there are two cables, then it is likely that the original socket is on a ring final circuit. But you would need to test if this is the case. you'll need a multimeter that can test resistance and mains voltage. Do you have one?

As it is a ring, it is best to add the new sockets and unclude them as part of the ring.
You can add a socket to a ring as an addition (known as a spur) but you can only have one spur. it is not permitted to have a spur from a spur.
Not true a Radial Final Socket Circuit will have 2 cables at all sockets, apart from the last one.
 
I was trying to simplify the process for the OP. That is why I said that it is necessary to test if this is the case.

I prefer to help the OP rather than snipe from the sidelines.
 
I was trying to simplify the process for the OP. That is why I said that it is necessary to test if this is the case.

I prefer to help the OP rather than snipe from the sidelines.
Nobody is snipping Mate you were giving misleading advice that's all it happens to everyone from time to time, no need to loose yer rag if you get pulled up once in a while.
 
If there are two cables, then it is likely that the original socket is on a ring final circuit. But you would need to test if this is the case. you'll need a multimeter that can test resistance and mains voltage. Do you have one?
@Taylortwocities doesn’t need defending but he stated it would need testing. Posts need to be read before opinions are given.
 

Reply to Some advice adding sockets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
880
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
244
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
727
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
825
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
722

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock