Discuss SSE DNO FIT potential problem 16A in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

M

marmaduke

I have a quote which I would like to go ahead with, but with the proposed cut off with fits, will the below system have any problems with SSE DNO and how would I complete the application form to ensure no problems as there is no space to state two invertors. or would it be safer to reduce by one panel to take total to 3610 watts.

3800 watts total

2280 watts one string, 950 second string power one 3.0 outd
760 watts Soladin 600

thanks

Darren
 
I would have thought you would be better using a power 1 3.6 which has 2 trackers. cheaper and easier.
SSE are interested in the inverter output so no problem putting a 4kw system in as long as it's allied to a 3.6kw inverter.
I haven't done the math to check your lower string against the minimum inputs on the power one though
 
thanks moggy1968 but info perhaps not clear enough 2280 string and 950 string different inclinations same direction - one at 35 other at 21 degrees

also typo on soladin should read 570 watts different direction to other strings hence two inverters

Darren
 
Last edited by a moderator:
the power one has 2 MPPT trackers so can handle different orientations and outputs. I'm about to put one on an install with 8 panels on a west roof, 8 on an east. it's aget out of jail inverter!!
 
The trouble is I have three seperate requirements due to orientation and inclination differences thus I need two inverters the question is will the combination of a power one 3.0 and soladin 600 be acceptable to my DNO with 3800 watts as could potentially go over 16A
 
If you mean UK Power Networks (DNO) then they are pretty adamant about the 16 amps (240 volts) limit. The SSE will only care what output you declare for FIT's. So keep it within 16 amps (3840w) on the commissioning form.
 

Reply to SSE DNO FIT potential problem 16A in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I'm not an electrician, just a householder (though do work in an area given a kick in the family jewels by government decision last year). I am...
Replies
12
Views
3K
S
I have number of options on location of panels, I wish to maximise generation as there is a Koi pond that uses 1 KW per hour 24/7 Possible...
Replies
4
Views
1K
R
Five days without solar but guess I haven’t missed too much yet, thanks to the grotty weather. I’ve had my solar installation since June 2011...
Replies
29
Views
4K
iconnect
I
S
With the recent proposals on fit changes I need to act ASAP preferred install is 2250w on sw ground mount 35 degrees inclanation, 1000w on sw...
Replies
0
Views
926
supersports
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock