@baldsparkies. The situation is dangerous when say you change an upstairs light for the customer in the bedroom for example. You turn off the upstairs MCB and then test for voltage. As youd expect thered be no voltage and you then begin to carry out the work. Once you have disconnected the core and seperated them, someone accidently turns on the 2 way switch for the landing light. One of the neutrals in your separated cables is now live and ready for you to touch =) that is why it is dangerous.
Live supply is linked from downstairs light and then travels to upstairs light, obviously if the switch is in the on position this will send a live supply through the lamp, down the neutral which you may have disconnected making it live.
I completely agree with you. The situation you describe is far from ideal.
The real answer, if your customer won't agree to re wiring the lighting circuit is to put both circuits with the shared nuetrals into one mcb.
That way it would be a departure from the regs at code 4 rather than a borrowed neutral situ code 2.
I can't remember the last time a borrowed neutral ambushed me. Or even what profanities I used to make others aware of my lack of approval.
As a competant person, you should never assume, cus it makes an
--- out of
U and
ME.
With domestic installs its easy to cover yourself ie check in advance identify and isolate as neccassary.
The borrowed nuetrals are out there right or wrong, sparky beware. If not you will learn, the hard way. Not a good answer I admit, but its a real world answer as many on the forum will confirm.
Oh yes it was an emergency lighting circuit in an office block, back in the 80s I believe. Thats the last one that got me.
Anyways, with all these people raving about rcd's you will only get a tingle if that. (Im such a bad lad, what a wind up merchant)
One other point, Non competant persons should not be touching the installation.
You are the sparky working on the lighting circuits, you are the sparky disconnecting the nuetrals, and to be fair you are the sparky who created the situation. It was safe before you started tampering, sorry but true.