Was fixing a broken twin florescent fitting today and came across something I couldn't work out.

First thing I did was measure the incoming voltage. At the fitting I measured L-E =190, N-E = 90v.

Scratched my head for a minute until I realized the Earth's coming in from the numerous (4) twin and Earth's didn't look right.

3 cpcs we're in a terminal block and the other cpc was direct into the fitting. I decided to try L-E at the terminal block and got 240v.

I sorted the wiring out so all the Earth's were in the fitting properly and all is good. However, I can't seem to grasp why the off readings. I was effectively measuring L-E (just the single cpc from a single t+e) when I got the odd readings but 240 when measured with the other Earth's.

Only thing I can think is either the single cpc was not connected to earth properly (poor connection) ??

Thoughts
 

Reply to Strange voltage readings - broken earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
615
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
844
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
989

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock