garty611

Hi all I have just had a 3920KW Sharp 16 X 245W panels fitted with a Solar River SR4K4TLA1 inverter.

There are 2 strings. One is currently reading around 330V and the other is just below 200V.

6 of the panels are landscape and 10 are portrait. I have since found out that 6 are on one string and 10 on the other.

Will that effect anything do you think or should the strings be matched in terms of input Volts.

The SolarRiver Product manual suggests that MPPT voltage range is between 200-500 V. The maximum DC Voltage is 550V. So therefore one of the strings falls below this minimum of 200V

Can anyone shed any light??
 
I'm not sure if the Solar River SR4K4TLA1 has two MPP trackers. If it doesn't, then you have problems.

The strings need to be the same if they are both installed on one MPPT.
 
I know its not the best system all round as I originally wanted 250W Sharp panels and a 3000 sunny boy inverter but it all changed when the Gov cut the FiTs... Has anyone had any experience with the SolarRiver stuff?
 
I've never used them.

However, if your installer has installed uneven strings and the inverter is indeed a single MPPT inverter then he has installed you a poor system. I've found a spec sheet but I'm not sure it is for the inverter that you have.

Having two inputs does not necessarily mean two MPPTs
 
I understand cheers BiggsSolar, I'm trying to get them back ASAP as the roofer set the strings without telling the sparks (i'm led to believe). I know now that they need to be sorted.
 
I know its not the best system all round as I originally wanted 250W Sharp panels and a 3000 sunny boy inverter but it all changed when the Gov cut the FiTs... Has anyone had any experience with the SolarRiver stuff?

I wouldn't worry about Sharp being the best, we've got Sharp and lots of panels we install often outperform them/ SB3000 is under spec for that size system too imo.

On a more positive note - you've got panels installed and although you need a bit of reconfiguring with the strings you're installed and hitting the 43p - happy days :)

It could be worse - you could be an installer. :rofl:
 
I wouldn't worry about Sharp being the best, we've got Sharp and lots of panels we install often outperform them/ SB3000 is under spec for that size system too imo.

On a more positive note - you've got panels installed and although you need a bit of reconfiguring with the strings you're installed and hitting the 43p - happy days :)

It could be worse - you could be an installer. :rofl:

No I've still got Sharp 245 I wanted the Sharp 250's but beggars cant be choosers this late on eh?
 
Some installers insist that landscape and portrait panels shouldn't be installed on the same string but I'm unconvinced. They definitely need to be on a 8 + 8 configuration.

To be honest, I would say that a lot of the installs that have been carried out over the last few weeks will have similar issues.

Standards and good designs appear to have gone completely out of the window.
 
Some installers insist that landscape and portrait panels shouldn't be installed on the same string but I'm unconvinced. They definitely need to be on a 8 + 8 configuration.

To be honest, I would say that a lot of the installs that have been carried out over the last few weeks will have similar issues.

Standards and good designs appear to have gone completely out of the window.

Cheers guys for all your help I'll keep you posted what happens!!
 
I was just wondering how are you measuring the voltages on the two strings, is it a function of the inverter? or are you simply turning off each of the DC isolators in turn. If the inverter has the ability to measure voltages on each string independently then it might have some clever optimization system even though the documentation I've found says it only has one MPP tracker.
 
I was just wondering how are you measuring the voltages on the two strings, is it a function of the inverter? or are you simply turning off each of the DC isolators in turn. If the inverter has the ability to measure voltages on each string independently then it might have some clever optimization system even though the documentation I've found says it only has one MPP tracker.

Good question... I was reading the Electricians meter whilst he was testing the system as originally he got the polarisation the wrong way around!! I may add that both strings are on the same DC isolator is that wrong?? Will it effect anything??
 
There are many ways to configure the isolators I always like one isolator per string, you say there are 4 DC wires going into the inverter so maybe its a 4 pole isolator?
 

Reply to Strings uneven MPPT Voltage in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I have 18 panels in 2 strings (37.8v open circuit voltage each) to be connected to a Fox H1 inverter. The manual says the below. Is the 600v open...
Replies
3
Views
823
Hi all. We have had 7x 400w solar panels for a number of years now on our roof which is se/nw facing end terrace. 4 on se side 3 on nw side...
Replies
0
Views
842
Hi guys, I am new to the forum so be nice! I used to install solar PV systems back when the tariffs were still good, and I've never had to go...
Replies
5
Views
5K
New to the forum. Retired Navy Aviation Electrician with 25 additional years in automotive electrical systems - enough knowledge to be dangerous...
Replies
1
Views
920
A question/advice requested re: solar panels (the context is a van/motorhome conversion)... I've got a question re: fusing/breaker for a solar...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock