Hi,
I have quoted up a job and would like to know if anyone can see anything wrong with my design.
From the 100A main cut out the tails go to an 80A switch fuse and out of there to consumer unit.
I need to run a sub main to provide another consumer unit upstairs,whiere there is a possibility of a further consumer unit if the client decides to make a 3rd flat. So my plan is...


1. remove tails from incoming side of 80A switch fuse and put in double pole henley block.

2. run tails from henley block back into switch fuse.

3. take additional feed from henley block into 63A switch fuse for sub main

4. run mains from out of switch fuse into new consumer unit upstairs.

all cable calculations have been done and comply for shock and overcurrent protection,so the main question i am wondering if it would be acceptable to install a 2nd 63A switch fuse for an additional ( 3rd ) consumer unit , either by henley blocking from 63A submain or from the henley block in position at the intake..( the 2nd consumer unit is already protected by a 63A switch fuse ).....i know there would then be no discrimination between the 2 63A fuses but something is telling me it will be ok as the DNO's main fuse is protected,hence it is a matter for the client......but i would invite the resident experts to ave a look at my plan and let me know if it is ok?
 
3 accommodation units
3 switchfuses feeding 3 CU's
seperate tails from henly blocks

if youre doing it like this then it will work fine.
not sure where your discrimination issues are as none of the switchfuses are in series ?
 
i assure you the cable calculations have been done and a seperate supply was my first suggestion but as usual the finances mean looking for an alternative to a new supply. original board is using less than 50 Amps and sub board will require approx 35 amps after diversity has been applied, so do you think this is a bad idea?
 
if there are gas boilers for heating & hot water then you should be ok
if its all electric heating , HW & power then no chance will 1 x 100A fuse stetch to 3 flats
 
3 accommodation units
3 switchfuses feeding 3 CU's
seperate tails from henly blocks

if youre doing it like this then it will work fine.
not sure where your discrimination issues are as none of the switchfuses are in series ?

i was under the impression dicrimination meant the local fuse operating as opposed to a fuse upstream?
 
Where are the 3 seperate meters going to be fitted, or is this a HMO type set up?
there wont be 3 seperate meters just potentially 3 seperate consumer units...maybe you got the impression of seperate meters by me describing them as flats,that is just how i am visualising the job but in reality it will not be seperate for renting out purposes so 1 meter and 1 bill is sufficient.
 
the only fuse upstream of the switchfuses is the service fuse and there is no requirement to discriminate with dno devices.

and so long as there are no mcb's bigger than 40A in the CU's , then you will have discrimination with the 63A switchfuses.
 
the only fuse upstream of the switchfuses is the service fuse and there is no requirement to discriminate with dno devices.

and so long as there are no mcb's bigger than 40A in the CU's , then you will have discrimination with the 63A switchfuses.
if as you say there is no requirement to discriminate with dno fuse then i have made a mistake in believing there was a requirement to do so,or maybe its good practice,as opposed to a requirement that you discriminate sub with main fuse?
 
i'd do as you say for DB2, but if and when you come to fit DB3, feed the tails from the henly blocks at the intake with a 2nd 63A switch fuse. then you won't have 2 63A fuses in series. and as biff says, max. 40A MCBs in DB2 and DB3.
 
i'd do as you say for DB2, but if and when you come to fit DB3, feed the tails from the henly blocks at the intake with a 2nd 63A switch fuse. then you won't have 2 63A fuses in series. and as biff says, max. 40A MCBs in DB2 and DB3.

that is the logical way forward,thank you for your help guys.
 
As you’ve applied diversity to the two sub boards loading and added to a real reading of 50A for the main board. You’re in trouble (in theory).

The thing I love about diversity is it’s the biggest load of codswallop out! BS88’s are about as subtle as a brick, that’s why I like them as well.
 
As you’ve applied
diversity to the two sub boards loading and added to a real reading of
50A for the main board. You’re in trouble (in theory).

The thing I love about diversity is it’s the biggest load of codswallop
out! BS88’s are about as subtle as a brick, that’s why I like them as
well.

diversity has been applied correctly and not in the manner you have incorrectly presumed
 
diversity has been applied correctly and not in the manner you have incorrectly presumed

What method of diversity have you applied to these separate CU installations??
I think Tony meant, that applying diversity is often a hit or miss affair, and unless you have many years under your belt in the industry, it'll be more often a miss than a hit!! The maximum demand diversity formulas you'll find quoted in BS7671 are the next best thing to being totally useless!!
 
Have to agree here; I split my house into loads of seperate RFC & lighting circuits. Went from a 5 way 3036 to a 12 way CU and all of a sudden I need my own power station!!!! But no additional demand. Crazy!
 
What method of diversity have you applied to these separate CU installations??
I think Tony meant, that applying diversity is often a hit or miss affair, and unless you have many years under your belt in the industry, it'll be more often a miss than a hit!! The maximum demand diversity formulas you'll find quoted in BS7671 are the next best thing to being totally useless!!

i have already said that diversity has been applied to the design of the installation,the way it has been calculated for this installation is as follows...
i have counted the lighting points and made a calculation based upon the presumed load,as opposed to just calculating 66% of the 6 amp circuit...i presume this is what you were referring to when you asked which method was used to calculate diversity?...same method of calculation was used for cooker and ring circuits...etc...(with their respective diversity allowances).
Is this acceptable?
 
i have already said that diversity has been applied to the design of the installation,the way it has been calculated for this installation is as follows...
i have counted the lighting points and made a calculation based upon the presumed load,as opposed to just calculating 66% of the 6 amp circuit...i presume this is what you were referring to when you asked which method was used to calculate diversity?...same method of calculation was used for cooker and ring circuits...etc...(with their respective diversity allowances).
Is this acceptable?

In a word ...NOPE!!

Calculating accurate max demand and diversity is an art, which takes a good amount of experience to master. Their are rule of thumb methods that many use, (often, myself included) but even those are not what you would or could call accurate!!
 
I'll avoid the diversity argument because I think Tony and E54 have a handle on that thorny issue already, and I personally hate the darned thing as i feel, like them two, it is exceptionally rarely applied accurately or properly and the blame for that lays squarely with the IET.

I am curious as why you have not suggested to your client to up-rate the supply to 125A (The majority of domestic installs are capable of this) and is a cheap upgrade. Then the out from this should go (If only one meter installed) to the meter, then to a DB with 1 Double Pole 80A MCB Type B installed for the main flat and two Double Pole 63A MCB's Type B installed, one for each living unit and you then run a sub-main/tails from this board to the individual consumer units. If at some point the individual units get their own meter then it is a simple matter to install sub meters to the outgoing ways just as we do in commercial sublet units but you keep the main meter to ensure all meter readings actually add up...

You end up with a nice neat and clean installation, fully compliant and you also stop one person overloading things to the point of killing all...(in theory anyway)
 
That sounds like the neatest way of doing it to me! Also probably the most functional way too in regards to adding additional meters at a later date.

I have never heard of a domestic i stall being upgraded to 125A though. Is it just a phonecall to the DNO and if so what is the cost? That is some valuable information right there Outspoken.
 

Reply to Sub board from sub main in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
457
Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
321
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Can you feed a consumer unit from another consumer unit, It would be supplied by a non RDC protected MCB. Is this allowed as I have always seen...
Replies
3
Views
2K
When doing an EIC for an additional circuit (which only covers that circuit), does the 'main switch/switch-fuse/circuit-breaker/RCD' section refer...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock