polo1

-
Arms
Reaction score
633
Domestic, three phase supply, one phase to each of three consumer units. Two consumer units are local to the intake, the third CU is on the first floor.
Currently the first floor CU is fed via a fused isolator at the intake. The replacement CU will be rcbos. However, we thought this submain was SWA, but discovered today that it is split concentric. Soo, looks like we now need to apply additional protection to the submain as it is buried in the building fabric.
We want to achieve discrimination with the 30mA rcbos in the new board, so is a 30mA time delayed rcd replacing the switch fuse acceptable in this situation?
Also, we would prefer to provide overcurrent/short circuit protection via a fuse, as opposed to an mcb. I recall there are fuse holders which fit on a DIN rail, but not sure of make/spec - anyone point me in the right direction?
Oh, it’s TNS, Ze of 0.34.
TIA
 
Fair point Westy, but our view was to have the submain meet current standards of protection.
You think it’s ok to leave as is?
 
Same here...the only way of realistically providing additional protection would be to have a 30mA RCD at the switch fuse. It would probably be more of a risk doing this if someone had to walk a couple of flights of stairs to go and reset it in the event of a fault....imo you are better of not providing additional protection to the distribution circuit and having the RCD at the far end.
 
Thanks guys, helpful.
Supplementary Q.... if you were providing o/c & additional protection to this submain, what setup would you use?
 
Thanks guys, helpful.
Supplementary Q.... if you were providing o/c & additional protection to this submain, what setup would you use?
You aren't left with a lot of choices unless the customer is willing to have the fabric of the building disturbed. The only real option you have is to have a 30mA RCD at the switch fuse end and a main switch board and circuit breakers at the end of the distribution circuit. If you were installing the distribution circuit from new you wouldn't even consider this option. If you assess the situation and take all risks in to account ...How likely is someone to nail/screw through the distribution circuit? Is it acceptable that the end user has to travel down a few flights of stairs to reset an RCD? Not to mention the fact you aren't working on the distribution circuit and only replacing the board at the end of it so there is no requirement for you to provide additional protection to the distribution circuit.
 
I’m my opinion there is an interesting question here.
Does a split concentric cable with its outer neutral conductor provide equivalent protection, if penetrated by a conductive object, to that of a cable with an earthed metallic screen or armour?
Particularly in the case of TNCS where neutral is reliably connected to earth at the cutout.

My train of thought with this is heading towards whether this would be a justifiable departure.
 
I believe although I maybe incorrect that these types of cable were deemed to provide protection when concealed in walls but it was later amended and removed. I am certain it was okay under the 16th Ed but disappeared from the 17th Ed.
 
also, if cable is buried, is it < 50mm from surface?
 
I would try to see if the distribution circuit cable is in the wall further than the 50mm eg in boxing/void as you are only changing C.U as said there is no need to RCD protect the cable if you did it would have to be a 30mA RCD which will give no discrimination if you want to provide some sort of RCD protection then recommend 100mA time delayed.
 
if its split concentric then the neutral is only really actually single insulated isn't it..... and we normally give single insulated conductors that arent in trunking etc a C2. Imo I wouldn't want to leave it personally
 

Reply to Sub main protection, views please. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Replacing DB’s with all singing all dancing RCBO’s Problem’s we have now…Existing installation consisted of DB Grd Floor.. DB 1st Floor…Grd Floor...
Replies
11
Views
1K
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
529
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
817

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock