Discuss SUB MAIN QUESTIONS. ADVICE NEEDED in the UK Electrical Forum area at ElectriciansForums.net

I had thought

I had thought about a TPN board, but was wary of the fact one of the DBs the 25mm armour feeds has a 10mm shower circuit, 10mm induction hob circuit, 2 ovens, few rings circuits, few lightening circuits etc. So 63A on the armour may not be acceptable?

Do MCBs not go upto 63A max? Would the above load on the DB not potentially pop the 63A? MCCB panel sounds more appropriate as you can use the 80A MCCB to give it some more juice, but it must’ve been too costly for the client, and that’s why the spark had bought the 80A switched fuses
Dunno, thats where design comes into play. To expand on the similar install. Although it was TPN in the plant room, because of the length of cable runs and TP loads, I had TPN board in plant room, submain TPN board on first floor, feeding 2 SPN submains also on first floor, TPN board in garage (submain off plant room) so for the house there were 5 DBs in total (and they were all stacked) - I think your concern about loading one phase up to 80A and they having a heat pump at 50A (bearing in mind how long there cycle is) maybe a bigger issue. Anyway its all about the design...
 
You get some 250A TPN boards that take a mix of wide 80-125A MCBs, and normal (17.5mm width) <= 63A MCBs from Hager. But you won't get decent selectivity that way with downstream DBs.

Going for a MCCB board would be the best option as then a incoming switch for all, and easy choice for any out-going protection from tens of amps upwards, along with reasonable (typically kA-range) selectivity on faults. Ideally put your SPD in there.

Fuses are good in many cases, but a busbar chamber and switched-fuses coming off is a bit of work and not likely cheaper than MCCB board, and MCCB boards are far easier for anyone to reset or to isolate stuff as needed,.
 
Use a main Three phase RCD CU to distribute a single phase to each floor/main area with a separate CU, at 100amps/phase it's not going to be a problem.
 

Reply to SUB MAIN QUESTIONS. ADVICE NEEDED in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Now that SPD's must be fitted regardless, how does this stand from a sub-main perspective? Went to look at a job and they want a supply to a pre...
Replies
3
Views
2K
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Replies
5
Views
2K
Hi, I have been tasked with a kitchen rewire. The current DB is fed by a 16mm armoured. There is a split load old contactum DB which I don’t...
Replies
4
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
556

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock