Discuss Suggestions for best way to wire underground supply please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

16mm swa buried is only 78 amps ambient temperature 20 degrees and that's without applying the 0.9 correction factor as cable is buried for ambient temperature for 30 degrees plus any other factors like depth etc
 
I always opt for the three phase rating with a three core but that is another debate but yes either way it is undersized if you use 16.0
 
16mm swa buried is only 78 amps ambient temperature 20 degrees and that's without applying the 0.9 correction factor as cable is buried for ambient temperature for 30 degrees plus any other factors like depth etc
Just trying understand - Table 4D4A for direct buried at 0.7m, ambient 30, ground ambient 20 and conductor 70 is 78A. So question is, why pick 30 ground temp to further derate to?
 
Last edited:
Just trying understand - Table 4D4A for direct buried at 0.7m, ambient 30, ground ambient 20 and conductor 70 is 78A. So question is, why pick 30 to derate to?
0.9 is applied where overload protection is required and prevents the cable going over temperature when overloaded.
The factor is used because cable ratings for cables in the ground are based on a ground temperature of 20 degrees compared with 30 degrees for other reference methods.
See regulation 433.1.203
 
which is all wrong. rarely will the ambient temperature rise above 20dg. C. in this country. once you are down 2 ft. underground the temp. is down to around 10dg.C.
 
IET Forums - Underground SWA Current Rating? - http://www.------.org/forums/forum/messageview.cfm?catid=205&threadid=27920
 
as an experiment, try shoving 100A down some 16mm for an hour. then measure the temp. of the cable. if you read >40deg.C. then your temp gauge is wrong. :eek:
 
we not in the sahara . not even spain. 30deg. my arse. we'd all be like essex boys at that temp. but with real tans.
 
haha, trouble is that the regs. are so pessimistic. written to cover arses. as a famous person once said." rules are for the strict adherence of fools, and for the guidance of wise men"
 

Reply to Suggestions for best way to wire underground supply please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi, I'm running a 70ft underground UF cable in 3/4 inch PVC conduit to 2 sheds. The sheds are 3ft from each other. I'm just a DIYer enthusiast so...
Replies
1
Views
757
Hi, I'm a DIY'er looking to build a 6x8 shed in my backyard in Colorado. I'm installing a gravel pad first, with 4 concrete Sonotube...
Replies
1
Views
336
Trying to find an armoured cable behind plasterboard and studding. It was used to supply power from the house but has been disconnected Can...
Replies
2
Views
434
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
444

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock