Discuss SWA armour supply to outbuilding, what CSA cable? and Reference Method? in the UK Electrical Forum area at ElectriciansForums.net

At 30m the volt drop would exceed the permitted maximum though..(going by the book)....though in practice we all know 6.0mm would be perfectly OK.
yeah, but OP has used 40A for his Ib. in practice 25 - 30A would be more realistic.
 
Seeing your nice pic has reminded me there is a run inside the house. If there's insulation involved that may add weight to the 10mm, or a bit more care to avoid it... Just saying :)

Another thought :

55mm x 55mm Cable Guard - 2Mtr Length - Black - https://www.tlc-direct.co.uk/Products/CG552BK.html?ad_position=1o4&source=adwords&ad_id=45425533757&placement=&kw=&network=g&matchtype=&ad_type=pla&product_id=CG552BK&product_partition_id=174053380627&test=finalurl_v2&gclid=EAIaIQobChMIz5emr6-u1QIViLvtCh355guSEAQYBCABEgLg7PD_BwE

IMG_0729.JPG
 
Last edited:
And I still don't know why you are thinking about running 10mm armoured in conduit. The steel armour inside is there to protect the conductors. Good luck getting armoured around a bend

The point is protect the cable from damage, any damage to the sheath allows water ingress which will rot the armour and make the cable unsafe.
The steel armour is there to connect a metal object penetrating the cable to earth, if the sheath is damaged and the armour rusts then it will no longer perform this function properly.

Luck is not required, just the correct sized conduit.
 
And I still don't know why you are thinking about running 10mm armoured in conduit. The steel armour inside is there to protect the conductors. Good luck getting armoured around a bend

The point is protect the cable from damage, any damage to the sheath allows water ingress which will rot the armour and make the cable unsafe.
The steel armour is there to connect a metal object penetrating the cable to earth, if the sheath is damaged and the armour rusts then it will no longer perform this function properly.

Luck is not required, just the correct sized conduit.
 
I've just calculated this and it IS 10mm, it can't be longer than your previous measurement and be a smaller conductor!!. If your friend says it's overkill, I hope can be at the enquiry with you to explain the fire

What fire are you predicting here? 6mm SWA has a ccc of 49A single phase clipped direct at an ambient temperature of 30c which is well above the nominal current of the circuit.
 
What you need to do is calculate your volt drops for the distribution circuit and the final circuits based on your design currents for those circuits.
The VD on the distribution circuit will add to the VD on each final circuit giving you three values, one will be for lighting and must not exceed 3% (6.9V) the others are non lighting and must not exceed 5% (11.5V).
Select your distribution cable based on one that complies in all cases.
Check that you are not likely to exceed CCC (very unlikely) or Zs limits.
E.g. If you had 230W (1A) of lighting/extraction on a 10m final circuit, two sockets each possibly taking 10A (very variable, normally you take the In for sockets) one at 7m and one at 12m and 15A for the AC on a 10m circuit then the calcualtion coudlba as the attached diagram.
Volt drop for 3 circuits.jpg
Note you have no short circuit discrimination between the supplying MCB and the final circuits, if you are installing 2 double sockets why is it a ring, a 20A radial may be easier.
 

Reply to SWA armour supply to outbuilding, what CSA cable? and Reference Method? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
850
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
970
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
522
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
591

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock