Search for tools and product advice,

Discuss Swa earth nuts in the Electrical Tools and Products area at ElectriciansForums.net

Ampo

-
Reaction score
15
Hi all, has anyone used these and are they worth it? Quite expensive but if they save time. I have a 2.5 swa run 50m down a garden to feed a socket, light and roller gate. I'm think of using these where I come in and out of the plastic socket amd plastic enclosures to bridge instead of comprising ip rating with a banjo.
Also is it still acceptable to just gland into the metal board on the feed end without a bango or one of these? I cant find anything in the regs saying no but heard some people are coding it down on eicr's. Cant see the problem if the casings earthed and paint scratched? Surely no different then taking an armoured into a galv conduit box. Any advise appreciated, always looking to improve without wasting mine and the customers time
Cheers
 
the nuts are brill. as for the earthing into a metal box, i'd always fit a earthing nut or banjo with a fly lead. reason being, once had a high Z on a feed cable to park home. cable was glanded properly but there was no continuity between box and earth bar inside. even though the earth bare was bolted to the casing, and paint removed at the sWA gland. Z reading came down from 100 ohms to 1.0 ohms .belt and braces.
 
Thanks all I'll grab some then. Yes I did mean earth lead, gland goes without saying but yes we've all seen them without! I'll fly lead on db end and then use them to bridge plastic boxes
Cheers for the help chaps
 
Earthing nuts are a no-brainer as far as I'm concerned. I've been using them for several years and will never go back to using banjos.
 
. I'm think of using these where I come in and out of the plastic socket amd plastic enclosures to bridge instead of comprising ip rating with a banjo.

Using a banjo correctly at a plastic enclosure doesn't affect the IP rating.
It will only affect it if you use it the same way as you would with a metal enclosure whether the bolt passes through the enclosure wall, this is wrong in a plastic enclosure as the plastic will flex/deform over time and loosen the connection. IF using a banjo in a plastic box the banjo must be trapped between two locknuts on the insideof the enclosure and the flylead bolted to the bajo only.
 
The earth nuts have at least two big advantages. First for plastic you can tighten sensibly with the "teeth" side to the plastic, not enough to not to crack it of course, and then lock using the set screw in the nut so it won't come free.

Secondly for metal boxes that are tarnished or painted you can again use the "teeth" to scrape the surface clean, then ideally remove and reverse the nut so you have a big contact area if high fault currents are possible. Again it is locked with the set screws once tight.

Using an earth lead is always a good idea (even with banjo) unless you are really sure the box-nut contact will remain in good electrical condition, and the box itself is going to be up to the fault currents possible.
[automerge]1584542238[/automerge]
Also if you need to seal stuff don't use the normal silicone that gives off acetic acid (vinegar smell) but use one that is safe against corrosion such as this one:
 
Using an earth lead is always a good idea (even with banjo) unless you are really sure the box-nut contact will remain in good electrical condition, and the box itself is going to be up to the fault currents possible.

I'm pretty sure the instructions for earhjijg nuts state that an earth flylead must always be used
 
Secondly for metal boxes that are tarnished or painted you can again use the "teeth" to scrape the surface clean, then ideally remove and reverse the nut so you have a big contact area if high fault currents are possible. Again it is locked with the set screws once tight.
I don't agree with that, at all. They are made for the teeth to 'dig' for a good earth contact, quite satisfactory for fault currents and a much better contact.
 

Reply to Swa earth nuts in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

I'm working on a system that has been installed incorrectly. It's a 3ph Hager board with 8 swa cables glanded into the bottom entry panel. The...
Replies
28
Views
3K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
I've an otherwise small and simple job to do later, out of hours, fit an outdoor IP FSU for a small AC unit fed from an outdoor socket on an RFC...
Replies
12
Views
2K
My Current Setup (see image BEFORE.jpg): The wiring for my existing detached garage is shown (see image BEFORE.jpg). The house consumer unit...
Replies
3
Views
3K
I have been asked to quote to install 6 x 1.8kW heaters to a wooden pergola with a perspex roof. It's on decking and there is a TN-C-S earth...
Replies
11
Views
3K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock