Discuss SWA Glands : Poor Fit in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
Background:

Served my apprenticeship 1964 to 1969 with NORWEB but not been directly employed in the industry since then.

I have just laid a 10mm 3 core SWA cable in a trench under the patio from the house to a detached garage 8.5m away. (cable run will be around 18m to 20m).

There won’t be much load in the garage other than lighting, sockets and an electrically operated door and possibly a router but I am making provision for a 7.2Kw Electric Vehicle Charging point, which will be a further 10m run to far corner of the garage from the garage consumer unit. I may also install more Solar panels on the garage so the supply to the garage may also at some point be a feed to the house. Battery Storage is also a consideration. There is no water feed or metal parts to the structure. Single brick construction, wooden roof beams and tiles.

My question is: As far as I can determine, there are two types of gland for use on SWA cable: indoor and outdoor.
For a belt and braces approach I’ve chosen the outdoor type even though both ends will be indoors. The recommended gland for 10mm cable is Niglon 25CW.
This gland has a compressible rubber/neoprene ring which provides the higher IP rating. However from the pictures you will see that it will never compress sufficiently to make a seal on the cable sheathing.

OD of Cable 18.9 (measured 17mm). ID of Compression ring 24mm.

I realise these glands are for a variety of cable sizes but the next smaller gland isn’t big enough for the 10mm cable and this one seems far too big.

Do I have to apply large amounts of tape around the cable sheath for the gland to compress? Or am I missing a trick?

I also have 1.5mm and 2.5mm SWA for sockets in various places around the rear garden for shrub lighting and an ultrasonic cat repeller. I currently have the internal glands (Niglon 20BW) which is a mistake as most of these will be used external. However these glands also seem too large also and I’m sure the external version will have the same problem compressing onto the sheath. I’m sure the shroud isn’t sufficient protection for an IP66 rating.

2nd Question: to conform to the new colour coding I need to sleeve the cores in Blue and green/yellow.

I have 5mm Green/yellow sleeving which will just about push onto a short piece of core but would take forever to do a long piece. I need some 6mm sleeving which doesn’t seem to be available from my normal sources.

Any suggestions?

Any advise welcome.

Ken

“The difference between genius and stupidity is, genius has its limits.”

DSC05841.JPG DSC05844.JPG DSC05845.JPG DSC05850.JPG
 
Those are the wrong size glands; the compression ring should be a much tighter fit.

I normally rely on my wholesaler to provide the correct size gland and cable. Where did you buy them.
[automerge]1568625657[/automerge]
The sleeving only needs to identify the cable. Doesn’t have to be over the whole length of cable. Have you tried some cable lubricant, to aid slipping the sleeving on?
 
Those are the wrong size glands; the compression ring should be a much tighter fit.

I normally rely on my wholesaler to provide the correct size gland and cable. Where did you buy them.
[automerge]1568625657[/automerge]
The sleeving only needs to identify the cable. Doesn’t have to be over the whole length of cable. Have you tried some cable lubricant, to aid slipping the sleeving on?
Those are the wrong size glands; the compression ring should be a much tighter fit.

I normally rely on my wholesaler to provide the correct size gland and cable. Where did you buy them.
[automerge]1568625657[/automerge]
The sleeving only needs to identify the cable. Doesn’t have to be over the whole length of cable. Have you tried some cable lubricant, to aid slipping the sleeving on?
I purchased them from TLC-Direct. Think they were recommended on the same page as the cable.
[automerge]1568626790[/automerge]
Those are the wrong size glands; the compression ring should be a much tighter fit.

I normally rely on my wholesaler to provide the correct size gland and cable. Where did you buy them.
[automerge]1568625657[/automerge]
The sleeving only needs to identify the cable. Doesn’t have to be over the whole length of cable. Have you tried some cable lubricant, to aid slipping the sleeving on?
Is there a special cable lubricant prduct?
 

Reply to SWA Glands : Poor Fit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
752
Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
840
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
517
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock