Discuss Switch fuse spures for combi boiler in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Numb

-
Reaction score
0
Can you run a 2.5mm twin an earth cable from the consumer unit to a 13A switched fuse spur then from that switched fuse spure on the feed side to another switched fuse spur so you have 2 switched fuse spures on one radial?? Reason for asking I’m getting a new boiler which is currently down my cellar but it’s going to be moved to my kitchen so I need a supply for the boiler or could I just flex out of the spur load side down my cellar up to the kitchen which would be a run of about 8m or should the boiler have the switch fuse spur more local to the boiler ?? Is ther any regs on this
 
There are no regs saying you need a fcu for a boiler at all, though boiler manufacturers suggest there are. The same boilers in Europe are plugged into a 16 a non fused socket with no problems. Boilers are internally fused anyway.
 
If your radial is from a 20a or less MCB you can have as many fcus or sockets as you like, but if it is from a 32a MCB (which probably also feeds a ring) you can only have one socket or fcu off it.
 
Can you run a 2.5mm twin an earth cable from the consumer unit to a.....

The OP is taking it from the consumer unit, so the breaker will have to be no bigger than 20A. Would also need notifying.
 
The OP has an existing radial (not specified) to a switched fused spur and wants to extend the radial to feed the new boiler position in the kitchen. Extend the existing circuit. As long as it complies with BS7671. The new switched fused spur is required for safe isolation to the boiler and 3A fuse to protect the external controls.
 
Would it be ok running a flex from the load side of the switch fuse spur down my cellar up into the combi Boiler in my kitchen? (Approx 8m run) would save me installing another spur, wasn’t sure if you had to have a spur local to the boiler can’t find no reg ther is no sockets neer wer the boiler is going in my kitchen and no spur way in the consumer unit to run a new circuit the spur down my cellar is on a 20a mcb in 2.5mm twin an earth only that spur on the circuit
 
Would it be ok running a flex from the load side of the switch fuse spur down my cellar up into the combi Boiler in my kitchen? (Approx 8m run) would save me installing another spur, wasn’t sure if you had to have a spur local to the boiler can’t find no reg ther is no sockets neer wer the boiler is going in my kitchen and no spur way in the consumer unit to run a new circuit the spur down my cellar is on a 20a mcb in 2.5mm twin an earth only that spur on the circuit
my advice is seek a local spark .
 
wasn’t sure if you had to have a spur local to the boiler

As I said:

There are no regs saying you need a fcu for a boiler at all, though boiler manufacturers suggest there are. The same boilers in Europe are plugged into a 16 a non fused socket with no problems. Boilers are internally fused anyway.

But you could run another fcu feed off the 20a MCB in the CU.
 
OK half the question answered. The other half was who?

If it was the owner he should not opening it. If it was a gas safe engineer he should know better and would quite likely fit the wrong fuse in the fcu as well.

At the end of the day you cannot protect against idiots.
 

Reply to Switch fuse spures for combi boiler in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
430
The new Advance Combi Boiler has a feed from consumer unit using 6mm cable on a 32amp breaker to a 45amp double pole switch. What size cable to...
Replies
9
Views
1K
Hi, I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the...
Replies
10
Views
874
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock