0
The Incoming breaker model is Terasaki - S250-PE, 250 Ampere Frame rated for which Ics is 70kA, Category A breaker

The outgoing breakers model is Terasaki - H125 NJ, 125 Ampere Frame rated for which Ics is 85kA,Category A breakers

The bus bar rating is 65kA for 1s.

How should this panel board be specified, 65kA for 1s??. Since both the Incoming & outgoing breakers are of category A breakers, Is it correct to mention the time rating along with the short circuit?

Generally, How is the panel board short circuit is mentioned in the name plate of the board for which the Incoming & Outgoing breakers have different breaking capacity?
 
What does the rating plate state and do you have the test certificate. They are normally rated to the busbar section withstand.
 

Reply to Switch gear / Panel board Rating in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Is it mandatory to have the bus bar rating equal to the Ampere Frame (AF) of the Incoming Breaker (MCCB) in the MCC, sub distribution panels. Is...
Replies
0
Views
736

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock