Discuss Telephone Slave help in the UK Electrical Forum area at ElectriciansForums.net

R

RyanCheetham

Good evening chaps, ran a slave socket off the master telephone point using contacts 3 and 5 as i always do, the slave socket will ring from an incoming call and has dial tone but will not make or answer a call. I am thinking maybe i need to connect terminal 2 as well but just after some clarifacation as i am not the best with telephones. Cheers guys
 
The client is trying to use 2 different sets of phones to save buying one bigger set. I wasnt sure if this would cause a conflict on the line but the client assures me it worked fine in their previous home
 
The line connections are 2 and 5, the bell wire connection 3 need only be connected if the client uses the old style phone(s) with a mechanical bell mechanism. If you client is using broadband on this phone line then disconnection of the bell wire throughout the installation is advantageous as it sometimes causes interference reducing the available broadband download/upload speed.
 
3 is the ring circuit, 2 and 5 are the A leg and B leg, so you need to connect 2,3,and 5 if you get 2 and 5 crossed over i.e 2 on master to 5 on slave then phone will ring whenever you pick it up,this is something I saw a few times and drives people mad, extension bells should be wired across terminals 3 and 5, if wired across 2 and 5 the bell coil completes a DC path and the line appears engaged.hope someone finds this useful.
 

Reply to Telephone Slave help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
746
Evening all, Need some telephone line advice - probably extremely simple... Is there a tool you can buy (other than an actual telephone) which...
Replies
12
Views
2K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Hi. Since the bad weather yesterday evening, we lost both telephone (i.e. no dial tone), and broadband. The cable comes up the wall outside, into...
Replies
5
Views
1K
Hello all, probably not the right forum but here goes anyway. My house phone wiring has become scrambled. I have the usual incomer with the...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock