Discuss Testing for borrowed neutrals? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
13
How would i test for borrowed neutrals?
Would it be a case of disconnecting all circuits neutrals at the DB and doing a continuity test between each neutral and seeing if any two circuits bell out?

hope it makes sense and i appreciate any feedback
cheers
 
close. you should IR test between neutrals, not continuity.
 
Cheers guys for response.
No stuart i havent got a particular problem at hand just trying to gain a bit of knowledge. Its one of those things you should identify as a tester before it makes itself apparent after a board change lol saves agro.
 
on an IR test you'd get a reading of 0.00 Mohms
 

Reply to Testing for borrowed neutrals? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K
Hi. I've read much about ac vs dc but can't find a 'simple' answer. If current alternates 50 times per second in a uk mains circuit, why do live...
Replies
23
Views
1K
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
660
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms...
Replies
58
Views
8K
Hi all, any advice would be greatly appreciated. Went to do some work at a factory unit on Monday ( changed 20 florries to LED battens and changed...
Replies
3
Views
603

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock