hi all I am currently working as a mate the contractor I'm working for which I shall not name does the following test.
he only measures zs doesn't do continuity r1 r2 he says that there is a good earth return if these results are within those permitted, he takes his ze from his zs to obtain his r1 r2 value,,now I am not saying I am right but shouldn't you prove a earth path exist before you power up to comply with ados ? The only reason I can see he does this is to save time but I'm guessing he is cutting corners views please or is this permitted.
 
you're correct. he's either lazy or incompetent (or both).
 
I have heard of this being used by the "£60 EICR" gang --- dont do the full checks but get your (R1 + R2) from (Zs - Ze). Saves time and gets the whole job done in 4 hours!!
 
Like all things in life unfortunately sometimes we can't carry out 100% of tests to the regs for various reasons if time and money no object. However these things need to be arranged as part of the limitations and agreements set out with the client when the job is arranged.
It's easy to slag people of but there is a difference between knowing what to do and having set parameters with a client


Personally I always advise testing to the guide lines but can't always get some one to agree the full cost of that so calculate R1, R2 for example.
EICR only though more thorough tests must be done on initials
 
It is perfectly acceptable to use a Zs test as a means of verifying cpc continuity on a periodic inspection, however you cannot deduce an R1+R2 value from this so I would expect to see that as a limitation (unless an R2 wander lead test had been done instead).
 
christ we hear some drivvel around here dont we...
to this half arsed chancer of a boss who thinks its appropriate to just energise without confirming its safe to do so then further more allows those who he is supposed to be influencing to witness such activities:

either do it rite or jack it in!!

and to them that were bleatin on about (R1 R2)...and not being able to carry out this test under certain conditions:

ever heard of a wander lead & method 2?

sinking feeling....
 

Reply to Testing question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
927
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
764
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
603

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock