You said it ran for two hours 2.07kW is the power 4.14kWh is the energy

1 calorie will raise the temperature of 1 gram of water 1 degree Celsius. (That's the definition of a calorie)
1 Calorie will raise the temperature of 1 Kg of water 1 degree C
I ltr of water weighs 1 Kg

So to raise 210 Litres from 8 degrees to 55 degrees requires 47 x 210 = 9870 Calories

1 calorie = 4.18 Joules
So
1 Calorie = 4180 Joules
1 Watt = 1 Joule/Second
In Simple Terms, 1 Calorie = 1.162 Wh

so 9870 Calories = 11469 Wh or 11.5kWh

(You asked ...)
 
I have installed a few of these systems and these are the facts:

Ambient air temp - 6 deg C
Water entering temp - 8 deg C
200l of water 8 deg to 55 deg = 2 hours
amp draw = 9amps

Now i'm no mathematician, but what does this calculate into?

Steve
200l at a little under 50deg temp rise needs around 11kWh of energy input.

9amps x 230 v = 2kW x 2 hours = 4kW

COP = 11 / 4 = 2.75

a COP of 2.75 at 6 deg c ambient air temperature is reasonable, but not particularly impressive for a heat pump tbh, though it at least demonstrates that it's considerably better than an immersion heater, and maybe just about on a par with a condensing gas boiler.

So possibly worth it for those on full electric heating.
 
Only one problem with all of this calculation. We do not know that the whole tank was at 8degC at the start. To do this you would need to run cold water through it until the outlet temperature was at this level. We do not know that the whole tank had reached 55degC. We only know that at the location of the stat the temperature is 55degC. As a tank should stratify, it is possible that the temperature is not uniform throughout. You would need to run a de-stratification pump until the temperature was uniform throughout the cylinder to know that the entire contents were at 55degC. When you have done this, come back and tell us what the energy input to the cylinder was and what methodology was used to verify the data in a manner suitable for peer review.
 
Only one problem with all of this calculation. We do not know that the whole tank was at 8degC at the start.( a guess would say it was colder, the cylinder had been stored over night in an un-heated garage. The morning of installation was at an ambient of 0 deg C and 6 deg C at the time of commissioning) To do this you would need to run cold water through it until the outlet temperature was at this level. We do not know that the whole tank had reached 55degC. We only know that at the location of the stat the temperature is 55degC. (I measured the water temp at each tap outlet throughout the house) As a tank should stratify, it is possible that the temperature is not uniform throughout. You would need to run a de-stratification pump until the temperature was uniform throughout the cylinder to know that the entire contents were at 55degC. When you have done this, come back and tell us what the energy input to the cylinder was and what methodology was used to verify the data in a manner suitable for peer review.

Sorry to reply quoting your text..

Steve
 
tbf though you';re asking installation companies for information that only the manufacturer could be expected to supply. AFAIK this data doesn't exist, which is why no supplier or installer can supply you with it.

the data supplied by steve k though is bit more detailed than most anecdotal evidence, it's just not been carried out under test conditions in a lab or verified externally, and a few bits of data are missing. As I read it he's stated that this warm up time is from cold on first filling the tank, therefore it's pretty much certain that the entire tank was at the temperature of the incoming supply when heating started. It's obviously not 100% accurate, but is likely to be in the right ballpark as long as the tank stat is placed in a sensible location such as the middle of the heating coil at the base of the tank.

I understand the desire for figures, but IMO some of those shouting down this technology are as bad the other way as the snake oil salesmen types in terms of giving the impression that the tech doesn't work at all, which is obviously false. This is a heat pump, as such it is proven technology that has been in operation in other forms for 50 years+, and there is zero reason to think that it won't work, or that a COP of 2.7ish isn't about right for the temperatures given. The technology works, that's not really in doubt (by anyone who understands heat pumps), the valid issue is the lack of accurate data to verify exactly how well it will work in different situations and for different uses, along with a decision from MCS over which category it should fall into for RHI etc (if RHI ever starts anyway) along with miss-selling by rogue marketing companies etc.

I do actually understand the difficulty for the manufacturers in supplying standard heat pump data though, as this is based solely on the air temperature, whereas these devices also collect radiated solar energy, and there currently are no standardised tests designed to measure devices that extract heat from both sources. I suspect that the cop of 2.7 would be the COP without significant radiant heat input from the sun, and that the COP would rise to more like 3.5-4 or higher with the addition of full sunlight giving an extra 1000W/m2 of energy input to the panel.

I really think that MCS are as much to blame here as the manufacturers, as these products have been available in the UK for at least 3-4 years to my knowledge, yet MCS seem to have just ignored them until they suddenly became the next big thing. Simply put, they're guilty of having been asleep at the wheel when they should have been proactively working with the manufacturers to device appropriate test methods and data requirements for these types of products since day 1 of MCS starting up.

That said, I have previously linked on this site to independent test data for one of these products, though the above caveats about it not incorporating solar input in it's figures would apply.
 
2.7COP is 0.2 above the accepted level published by the EU for the definition of renewable heat.

Heat pumps do work, but recent studies by the Energy Savings Trust shows that in a very large number of installations house holders were gaining no benefit for a large variety of reasons including design, specification, installation, heat emitter type and user interaction. There is real danger that without the kind of data I constantly ask for there will simply be an action replay of this kind of experience.

With heat pumps, it is horses for courses. Currently they are not an appropriate technology for all properties in all locations. The level of expertise to correctly assess and specify systems is in my opinion far higher than that needed for PV, ST, or installing a normal central heating system. The margin for error in all of them in far greater.

Sadly, to say you suspect something in terms of performance is not substantive. Would you be comfortable and more importantly legal going out and selling on such a basis?

There are other manufacturers of hybrid equipment who are in dialogue with MCS over their equipment to clarify it's position in terms of registration. Why was this so difficult for the manufacturer's of thermo dynamics? Why was something registered as a solar panel tested with ethylene glycol then sold for use with refrigerant in something that is clearly a heat pump?


If you go back and check in early threads on this kit, my interest was originally in performance data because I liked the look of it, and it appeared to promise something new. My interest was in the claims for space heating, principally for off-grid areas. My increasing disenchantment is because no one has been able or willing to provide the information.

If the manufacturers had gone to MCS with chapter and verse on the equipment four years ago, all the issues now raised could have been dealt with then, but it appears they did not. Issues surrounding compliance with the Building Regs and required competencies could also have been sorted. The equipment was registered under solar keymark, in a way which was not appropriate. If the equipment works as described, why would you do that? Registration only existed because this scheme is recognised in the UK as an equivalent to the MCS product scheme. It would be interesting to know what is happening to it's registration under Solar Keymark in light of the intervention by MCS.

DECC will decide whether this equipment is eligible for RHI and in what category, not MCS.

The issue of whether this equipment works in a cost effective manner in cooler climates is still unanswered. Why is it so difficult for the manufacturers to provide substantive performance data of this nature and verify the claims made? Facts speak louder than words. All we have had are words.
 


Introducing
the NEW Magic Thermodynamic Box, its a lean green hot water machine!



Delivering
hot water @ 55 degrees, 24/7 with a cop rating from 1 in 3 to 1 in 7!



 
I just don't get it.

Without going into technical details and empirical data ect ect....all these panels can do in a normal house is heat tap water to 55 degrees.

Now the EST in conjunction with DEFRA published a report entitled "Measurement of Domestic Hot Water Consumption in Dwellings". The samples 124 houses over a set period.

The report is incredibly detailed with loads of cool graphs and stuff and runs to 62 pages (email me if you'd like a copy)....but long story short they found the average spend per year on domestic tap was was at that time £105.

So say these panels save me £105 off my oil or gas...I still then have to pay for the electricity to run the compressor which appears to be about £8 a month....So the net saving cannot be more than £50 a year.

So why would I spend £5000 on something that is going to save me £50 a year.....

Or am I missing something...
 
I asked a question but as many others have been ignored.
So, the cost of heating my hot water per year is around £140 (it may be a little either way) So to install a system that costs £5000 + running costs does not make economical sense, even if it meant my hot water would be totally free, which of course these systems do have running costs, but let's just say it halved my hot water running cost, that would be 35 years to recoup my initial outlay, plus another 17 1/2 years before I am in profit so a total of 52 1/2 years...

Of course there may be the RHI, which IF it ever happens and IF this system is included in the scheme may help.
I am not disputing whether it works, I am sure it does to some degree but the sums just do not add up at all, or am I missing something here?

I must learn to type quicker, someone beat me to it, strange though the figures are similar....
 
Completely agree with Earthstore........I just don't get it......

If you sat down with a customer and told him the system would take 35 years to recover its costs and and 17 to be in profit......how many do you think would go ahead.....

Can this product be sold ethically......I wonder
 
Great news chaps, just realised if I buy one of these systems I could celebrate my 100th birthday with the fact that I had broken even. :cake:
 
I asked a question but as many others have been ignored.
So, the cost of heating my hot water per year is around £140 (it may be a little either way) So to install a system that costs £5000 + running costs does not make economical sense, even if it meant my hot water would be totally free, which of course these systems do have running costs, but let's just say it halved my hot water running cost, that would be 35 years to recoup my initial outlay, plus another 17 1/2 years before I am in profit so a total of 52 1/2 years...

Of course there may be the RHI, which IF it ever happens and IF this system is included in the scheme may help.
I am not disputing whether it works, I am sure it does to some degree but the sums just do not add up at all, or am I missing something here?

I must learn to type quicker, someone beat me to it, strange though the figures are similar....

the same applies to solar water heating systems though, and folk do still get them installed as well for a multitude of reasons.

I think the price point really should be about £3.5k for an installed water heating only system, which makes things a bit different, and I reckon the main market for this ought to be in new builds, or situations where they need a mains pressure tank anyway , which is circa £1k inc fitting, so the thermodynamic element is only £2.5k, and with oil / electric heating and no need to pipe the boiler / heat pump output to the
 
I'm probably missing something obvious here but what is the advantage of using a solar panel instead of having a standard finned evaporator with a fan? When it all boils down to it all heat pumps are solar powered, with an old fashioned evaporator the sun heats the ground, the ground heats the air and the air evaporates the refrigerant giving it latent heat.

I have a refrigeration question as well, how does the solar panel heat pump prevent the superheat figures of the refrigeration system going off the chart on a hot day?
 
I'm probably missing something obvious here but what is the advantage of using a solar panel instead of having a standard finned evaporator with a fan? When it all boils down to it all heat pumps are solar powered, with an old fashioned evaporator the sun heats the ground, the ground heats the air and the air evaporates the refrigerant giving it latent heat.
it can draw heat both from the air and from solar radiation falling on the panel, an ASHP can only draw heat from the air, so in theory it should have a higher COP when it's sunny, and a similar COP when it's not.

no fan and less moving parts ought to also mean a longer life, and certainly less outdoor noise.

I'd expect they'd be a better option than ASHP in some situations and not in others, but they should be a valid option IMO.

I have a refrigeration question as well, how does the solar panel heat pump prevent the superheat figures of the refrigeration system going off the chart on a hot day?
there's no insulation on the panel, so it will presumably max at out around the 60-70 deg that PV panels max out at in the UK even when stagnating. I assume the refrigerant is ok to cope with this, but haven't looked that far into it / found those figures.
 
it can draw heat both from the air and from solar radiation falling on the panel, an ASHP can only draw heat from the air, so in theory it should have a higher COP when it's sunny, and a similar COP when it's not.

no fan and less moving parts ought to also mean a longer life, and certainly less outdoor noise.

Gavin, Are you going to replace your current water heating system with Thermodynamic solar?
 
Last edited:
Gavin, Are you going to replace your current water heating system with Thermodynamic solar?
no.

I installed a solar water heating system 4 years ago which should be good for 30 years or so, I'd be pretty silly to replace it now.

If I were off the gas grid though, particularly if I was using electric for water heating, and didn't have a solar water heating system already, I'd probably install one of these panels plus solar PV. That's the sort if situation I see these possibly working in if the price was right, though I'd expect it'd need RHI payments to make it really financially viable.

- - - Updated - - -

that and new build eco homes off the gas grid.
 
btw, when I say this is likely to be better than an ASHP, I should probably point out that I don't advocate using ASHP's to replace condensing gas boilers either, as an ASHP is currently higher carbon than a condensing gas boiler for water heating.
 
there's no insulation on the panel, so it will presumably max at out around the 60-70 deg that PV panels max out at in the UK even when stagnating. I assume the refrigerant is ok to cope with this, but haven't looked that far into it / found those figures.

60-70 deg on the evaporator is very very high compared to standard refrigeration systems. The negative effect this will have is on the compressor, not the refrigerant itself. I would have grave concerns about the the long term reliability of this system.
 
Its is good to see some more technical discussion of this technology, even without firm performance data. At the other end of the scale, how is this equipment going to avoid icing and what defrost cycle is available?

The running costs element is critical to its viability. Normal Solar Thermal has zero costs for energy production and pretty low running costs - a fluid change every five years and a pump if you are unlucky during it's lifetime. Properly designed and installed it will provide 50-55% of an annual hot water requirement. In some parts of the UK, this figure can be higher. This is the cost comparator. The cost of the fuel for auxiliary water heating enters the equation. As alluded to in this thread true running costs for thermo dynamics in UK conditions is currently unavailable.

There is a lot of hard work going on with DECC to make normal ST viable under the proposals for the RHI. If this is successful and IF the questions raised about thermo dynamic equipment can be answered by the manufacturers, then at some stage it may be included. However, the complexities currently involved in the RHI consultation over issues such as bi-valency, and issues surrounding what this technology is finally defined as may still exclude it.

I think the one thing the opinions expressed in this thread shows is the true market for appropriate use of this equipment IF it's performance can be validated is very very small. Use in conjunction with other technologies means it would need to to be compatible with a multi-coil thermal store or hot water storage vessel, not just a dedicated tank. If it is not compatible, you are possibly in to a two tank design, with all the space implications that entails.
 
I have a refrigeration question as well, how does the solar panel heat pump prevent the superheat figures of the refrigeration system going off the chart on a hot day?

The gas isn't in the evaporator long enough for it to be affected by the outside temperature.
When I commissioned the system I first posted about the systems had a saturated suction temperature of -12 deg C and a pipe temp at compressor inlet of 4 deg C, giving a compressor superheat of 16k. I didn't measure the evaporater superheat as the pipe run was so short.
I would not expect this to change whatever the weather / ambient conditions.

**Edit**

Colder outside temps could cause more problems for the refrigeration system than the hot. This is due the possibility of un-evaporated liquid refrigerant finding it's way back to the compressor.
To get around this possible problem, the systems I have installed have the suction line coiled around the compressor to boil off any remaining liquid refrigerant.

Steve

Steve
 
Last edited by a moderator:
DSC_0035.jpg

a pic to illustrate

Steve
 
how is this equipment going to avoid icing and what defrost cycle is available?

It can't....if you were to incorporate a hot gas defrost system into this, as in a commercial freezer, the refrigerant would shoot through the evaporator at about 70 deg C, the same as the hot surface temperature discussed in another post at a pressure of appx 300psi.

I have pressure tested the evaporators at 250psi with no ill effects.

Steve
 
60-70 deg on the evaporator is very very high compared to standard refrigeration systems. The negative effect this will have is on the compressor, not the refrigerant itself. I would have grave concerns about the the long term reliability of this system.

The compressor regularly deals with temperatures like these, it's what they do. Compress low (temp)pressure gas into high (temp)pressure gas.
It is this hot gas that heats up the water.

Steve
 
60-70 deg on the evaporator is very very high compared to standard refrigeration systems. The negative effect this will have is on the compressor, not the refrigerant itself. I would have grave concerns about the the long term reliability of this system.
that would be stagnation temperatures though, ie when the compressor wasn't running, and that would be extreme top end. tbh I've never known PV panels to get anything like that hot in the UK, usually more like 50-55 deg top end due to the air cooling which this will also have. Thinking about it some more, I'd expect these panels would stagnate at a lower temperature than that due to it's greater surface area (fins) and conductivity to the rear of the panel for greater cooling of the rear (back of a PV panel can be around 35deg while the front is at 50 due to the poor conductivity, I'd expect this to be far more even in an aluminium panel, so the heat loss to air on the back would be that much greater).

In operation I'd be surprised if it ever went much above 25-30 deg flow temperature into the compressor even in full sun, though this depends on the flow rate and return temperature.
 
Steve
Thanks for your knowledge and honesty in these replies. This is really refreshing in trying to get to the bottom of the efficacy of this equipment. From your reply, does in your opinion this mean there is a minimum ambient temperature at which this equipment should operate? Is there a point at which there is no energy gain for the energy input to run the system? I had been told the COP effectively fell to one at around this temperature, which would mean an auxiliary back up source of water heating would then be more effective if in terms of energy cost (eg gas) if it was cheaper than electricity.
 
Last edited:
In operation I'd be surprised if it ever went much above 25-30 deg flow temperature into the compressor even in full sun, though this depends on the flow rate and return temperature.

If you ever saw this kind of temp flowing into the compressor, you need to call a fridgeman. Your expansion valve is knackered.....:D
 
From your reply, does in your opinion this mean there is a minimum ambient temperature at which this equipment should operate?

R134a boils at -26 deg C, given that you need appx 10k superheat to get a refrigeration effect, this would suggest that the systems will function at -15 degC ambient
 
Its is good to see some more technical discussion of this technology, even without firm performance data. At the other end of the scale, how is this equipment going to avoid icing and what defrost cycle is available?
Actually I reckon that where used for water heating only at least it doesn't need a defrost cycle, as it's probably simpler and more cost effective to just switch to immersion if required once the COP becomes lower than 1:1, then rely on the sun to defrost the panel - this is one advantage these systems have over ASHP where the sun will never defrost the ASHP while outdoor air temps are low, whereas I'd expect the sun would be able to defrost these panels fairly quickly even in -10 ambient air temperatures, which I've certainly seen happening with PV panels.

The running costs element is critical to its viability. Normal Solar Thermal has zero costs for energy production and pretty low running costs - a fluid change every five years and a pump if you are unlucky during it's lifetime.
not entirely true - the electricity to power the pump can easily cost £5-10 a year depending on the set up, efficiency of the pump etc. Unless it's a PV powered pump, or I guess if the customer also has solar PV installed.

There is a lot of hard work going on with DECC to make normal ST viable under the proposals for the RHI.
snigger... the same numpties who killed the solar thermal industry immediately the tory government got into power by pulling the plug on the previous grant scheme then taking 3 years to fail to implement RHI? That's not my definition of hard work to make ST viable, quite the opposite, but yes maybe they will eventually come up with something that makes it viable again.

I think the one thing the opinions expressed in this thread shows is the true market for appropriate use of this equipment IF it's performance can be validated is very very small.
I agree that it should be a niche product,but I'm not sure I'd agree on the size of the potential niche being 'very small'.

all new houses by 2016 ought to have the sort of low energy requirements that would make this sort of technology potentially viable for both heating and hot water purposes as long as the government doesn't water down it's plans any further (ok, maybe only the smaller houses / flats, with ASHP being more suited for larger houses). That's a 100,000 houses a year potential market for both water and space heating, or for water heating alone.

There's also around 500,000 homes that are all electric heated, where this would almost certainly be a cost effective alternative for the water heating side of things at least (if installed at a reasonable price), and surprisingly, that number has been risking over recent years due mainly to the number of flats / 'studio apartments' being built with such low heat demands that they're opting for all electric heating to save the expense of a wet gas heating system. I'd think that many of these stuido apartments could well be candidates for themodynamic panels to be viable cost effective alternatives for both water and space heating, where there's only 1-2 rads and low heat requirements due to only 1-2 external surfaces with reasonably high insulation values.

I'd also think this could be a particularly viable option for water heating only for those with PV installed where the running costs could be close to zero if the water is set to heat only during the day.
Use in conjunction with other technologies means it would need to to be compatible with a multi-coil thermal store or hot water storage vessel, not just a dedicated tank. If it is not compatible, you are possibly in to a two tank design, with all the space implications that entails.
that entirely misses the advantage these systems have over solar thermal in that they do not need a secondary heat source other than an immersion for the very few days of the year when the system can't operate due to extreme low temperatures. So no they don't need a second coil to be combined with another heat source.
 
ST panels get way hotter than this during stagnation, hence the avoidance of soldered joints. Temperatures can exceed 180degC.
yes, but they are insulated from the air, this panel is specifically not insulated at all, quite the opposite, it's highly conductive to air as it's entirely made of aluminium.
 
If you ever saw this kind of temp flowing into the compressor, you need to call a fridgeman. Your expansion valve is knackered.....:D
oh erm, right, sorry I've not hugely looked into the exact functioning of the heat pump side of things, tbh I don't think I've seen a proper diagram of how they're laid out, and I've not actually worked with heatpumps (at least not the internal side of them).

I'll bow to your knowledge on that side of things as you're actually installing the things from the looks of it.

Do you have any data on what the operating temperatures of flow and return from the panel actually are in operation in full sunlight? Knowing this would help greatly to understand the likely efficiency of the panel in terms of absorbing heat from sunlight vs losing a proportion of that heat to the atmosphere if the panel's operating hotter than the surrounding air. If the panel is operating at lower temperatures than the surrounding air even in full sunlight, then the panel should be in the region of 90-95% efficient at the conversion of radiant solar energy into heat depending on it's absorption factor / efficiency.

I'd generally been assuming they'd lose some of this heat to the air, but looking at your figures earlier, it looks fairly obvious that they must actually still be absorbing heat from the outside air as well, which means they must be operating below ambient air temperatures, and therefore not be losing solar energy to the air at all.

In which case my assumptions behind my guess of maximum operating temperature are obviously way off as this would be below the maximum ambient air temperature not above it.
 
Your missing the point of heat pump operation they dont use the sun the defrost, they use hot gas to defrost and the buffer tank will aid the heating system while they defrost.
 
The thermo dynamic panels only require small amounts of heat to operate, the heat comes from the compressor to warm the water, not the panel.
the compressor doesn't create heat*, it merely concentrates it from a lower grade to a higher grade of heat. The original heat energy input that allows for the high COP's comes from the panels extracting heat / energy from the air and solar radiation.



*actually I suppose it does to an extent in terms of directly transferring electrical energy to heat, but that's not where the bulk of the heat comes from.
 
Heating and cooling is accomplished by moving a refrigerant through the heat pump's indoor and outdoor coils. Like in a refrigerator, a compressor, condenser, expansion valve and evaporator are used to change states of the refrigerant between a cold liquid and a hot gas.
When the liquid refrigerant at a low temperature passes through the outdoor evaporator heat exchanger coils, ambient heat is used to cause the liquid to boil. This boiling or change of state process amasses energy as latent heat. The vapor is then drawn into a compressor which further boosts the temperature of the vapor.
Passing into the building, the vapor enters the condenser heat exchanger coils where it transfers heat to indoor air, which is drawn across the coils by a fan. As the vapor cools, it condenses back into a liquid, and releases its latent heat to the air passing over the condenser unit.
Exiting the condenser, the cold liquid refrigerant is under high pressure. The refrigerant passes through an expansion valve which reduces the pressure, draws in heat and allows the refrigerant to re-enter the evaporator to begin a new cycle
 
not if your using gas it dont
basic laws of thermodynamics say you're wrong.

the additional heat energy on top of the electrical input energy isn't just magicked into existence by the compressor, it has to originate somewhere, and in the case of a closed loop system like this that heat input obviously has to come from the panel absorbing it from the air and sun.
 
The panels wont reach 55 degrees if the outside temp at night is -5. Thats why ASHP can work down to -20,
I'm fairly obviously not saying that the compressor doesn't extract the heat energy and boost it up to the required temperature, but you seem to be denying that the heat energy actually has to originate in the panel, which is obviously wrong.
 
energie 4 block thermal graph.JPG

I've now found a datasheet for the larger swimming pool / heating systems at least.

It doesn't give proper COP figures, but does at least give min / max electrical input and heat output figures eg for the 4 panels system, as well as diagrams showing the actual heat output expected from different ambient air temperatures in day and night. I don't know what sunlight levels are assumed in the daytime heat output figures, I'm thinking probably they're based on best case scenario of 1000W/m2 insolation, but it doesn't say.

Absorbed Power 0,9 - 1,8 kW ; Thermal Power 3,6 - 7,3 kW
 
Yes but only a few degrees, stick the panel in the ground or lake it would still work, how do you think fridges work or cold stores, freezes.
it's not a matter of degrees as such, it's a matter of total energy input into the system. and yes you could put the panel in a lake if you had one, but this is an alternative for those of us who don't have sufficient lakes or ground for a GSHP / WSHP to be an option.

It has occurred to me that we might be both arguing the same position but using different terminology.
 

Reply to Thermo dynamics for hot water that runs off atmosphere in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Replies
10
Views
2K
HI Folks. This is my first post so apologies if it's in the wrong location. I recently installed a 3kw Solar system with an iboost diverter...
Replies
15
Views
5K
Hello everyone my name is Tarek, i work as a concert and show lighting operator with over 20 years of experience in this field, so i have gained...
Replies
1
Views
2K
Hey everyone - new to this thread so thanks for having me. I have an issue with my DC power in a small truck camper. I have 3 accessories plugged...
Replies
5
Views
1K
Apprentice electrician (coming towards the end of my 1st year) here and looking for some help and understanding. I have moved into my flat and I...
Replies
53
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock