Hi i have just bought a lathe which is running on three phase i have bought a vfd to run the lathe from single phase

but i have a coolant pump that runs on three phase i have converted it to run on single phase but it appears to have a dip when running do any of you guys know what i need to do.

here the video clip

20171012_113802.jpg
 
So the lathe runs from the vfd but the pump does not, correct. How exactly have you "converted" it to run from single phase?
 
Looks like he's connected a capacitor across the terminals to create a phantom 3rd phase , usually the motor must be connected in delta but that doesn't look like a dual voltage motor so I would say that's the problem the motor will be running a lot slower than it usually does. Winding street must be intarnaly connected in star configuration as only 3 leads visible.
 
Didn't see the capacitor!
Well it will run but the efficiency and power will be reduced as the shift and/or phase voltage balance will never be correct by doing that.
 
You can get away with it with a small dual voltage motor connected in delta, giving 230 to each winding, but that motor will only be getting 115- 120v per winding connected in star.
 
So the lathe runs from the vfd but the pump does not, correct. How exactly have you "converted" it to run from single phase?
Hi i bought this and this runs great just got it working only down side is you loose all the original controls on the lathe but it all run on three phase and my house is only single.

putting a single phase motor on it would not of work because the electrics was all wire up for three phase

s-l500.jpg

20170928_142621_HDR (1).jpg
 
You can get away with it with a small dual voltage motor connected in delta, giving 230 to each winding, but that motor will only be getting 115- 120v per winding connected in star.
Yes the pump is star only so i was told wiring it like this would only give me half the power which should be fine but my concern was the way it was running or is this common doing this will it run like this or just burn out??

i thought it may be dipping in power because of the capacitor no big enough???
im not sure i have never done this before just going of advice and forums.
 
2.5 is a bit small, usually thy are about 40uf
 
Looking at other forums that seems correct, not sure if using say a 3uf would improve things. You could try and find the star point of the windings and separate to you can connect in delta, things would be a lot smoother.
 
Yes you would have to strip it down to find the star point, it would have been made with 3 sets of windings so there will be a star point, it could be there as soon as you take the top off. Just depends how able you are, you could then reconfigure internally and bring out the 3 leads as it is just now.

It seems to be pumping sufficiently anyway, you'll never need that kind of flow for coolent on the lathe, it'll empty before it's drained back. You'll use it once and it'll be everywhere, I hardly use my collect pump, only if it's stainless steel I'm turning.
 
Yes you would have to strip it down to find the star point, it would have been made with 3 sets of windings so there will be a star point, it could be there as soon as you take the top off. Just depends how able you are, you could then reconfigure internally and bring out the 3 leads as it is just now.

It seems to be pumping sufficiently anyway, you'll never need that kind of flow for coolent on the lathe, it'll empty before it's drained back. You'll use it once and it'll be everywhere, I hardly use my collect pump, only if it's stainless steel I'm turning.
its was they surging it was doing im concerned about the flow is ample i think you will have to turn it down
 
Never considered it to have 400v windings connected in delta, wouldn't that be unusual for such a small motor?
 

Reply to three phase coolant pump in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
Hi. I have a single phase water pump which supplies our house. It frequently cuts out and needs to be reset (on pump itself). Because of our...
Replies
3
Views
494
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
845
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
303
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
667

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock