Discuss time delay rcds in the UK Electrical Forum area at ElectriciansForums.net

A time delayed RCD should always be used if other RCD's / RCBO's are connected after them.

This will allow the other RCD's to operate before triggering the time delayed RCD.
These are generally used in TT installations as the main switch when 30mA RCD's are also used for socket outlet circuits.
 
Last edited:
As Adam has stated, S type RCD's will always be required for reliable discrimination with downstream RCD's/RCBO's. The other recommendation is that the upstream RCD device be at least 3 times that of the downstream, well let me tell you now, that rarely if ever works!! Time delay is the ONLY means of achieving discrimination between RCD devices!!
 
Guys, at the risk of going a bit of topic can I expand the question a bit?

What if you are fitting a 100mA RCD to protect a TT installation where there are no other RCDs currently fitted to any circuits? Would you....
a) use a non time delay RCD because they are cheaper and you don't have any other RCDs to require discrimination or
b) use a time delay so upgrades to circuits in the future can be done by adding 30mA RCDs without causing a discrimination problem

This is actually a situation I am quoting for at the moment. Customer doesn't want the cost of a CU upgrade (which I have recommended to give 30mA on sockets, bathroom etc etc) but currently has no RCDs and a Ze of about 50 ohms which I have told him isn't giving him any fault protection.
btw. for what it is worth I have gone for option b).
 
Well use a S Type delayed as the main switch, that's a saving on a main switch, and a 30 Ma RCD on those circuits that require it, which without knowing the job is all of them possibly, I don't want to come across as critical your not insisting on RCD protection on a CU change ? and don't forget also the enclosures type needs to be a class 2 or all insulated for TT's as I interpret the regs
ATB J
 
Well use a S Type delayed as the main switch, that's a saving on a main switch, and a 30 Ma RCD on those circuits that require it, which without knowing the job is all of them possibly, I don't want to come across as critical your not insisting on RCD protection on a CU change ? and don't forget also the enclosures type needs to be a class 2 or all insulated for TT's as I interpret the regs
ATB J

I think you misunderstood me. I was not quoting for a CU change. The work asked for was an outside socket off another, RCD protected, CU. I just noticed that the main CU supplying most of the house circuits didn't have any RCD protection and told the guy that wasn't clever. Not suprisingly the guy doesn't want a £100 job turning into a £500 job with CU change so wants the minimum that will give him some protection. That would be an up front 100mA RCD without touching the main CU.
 
I think you misunderstood me. I was not quoting for a CU change. The work asked for was an outside socket off another, RCD protected, CU. I just noticed that the main CU supplying most of the house circuits didn't have any RCD protection and told the guy that wasn't clever. Not suprisingly the guy doesn't want a £100 job turning into a £500 job with CU change so wants the minimum that will give him some protection. That would be an up front 100mA RCD without touching the main CU.

Sorry dude got wrong end of stick, just note it on the minor works to cover your ---

ATB J
 
Sorry dude got wrong end of stick, just note it on the minor works to cover your ---

ATB J

don't apologise, I didn't exactly make it clear in my first post! ;)

Yep, arse will be covered but it looks like I have persuaded him to have an up front RCD fitted so at least he will get some protection.
 
If you are installing a socket-outlet to be used for mobile equipment outdoors, then the socket-outlet will require 30mA RCD protection.
The problem you have with installing a time delayed up front RCD, is what delay you will use.
1s for distribution circuits, or 0.2s for final circuits?
 
If you are installing a socket-outlet to be used for mobile equipment outdoors, then the socket-outlet will require 30mA RCD protection.
The problem you have with installing a time delayed up front RCD, is what delay you will use.
1s for distribution circuits, or 0.2s for final circuits?

I don't think I am explaining myself very well :(

The outside socket is actually on another CU which also supplies some sheds and garages. This already has RCDs so I don't actually have to do anything to meet the regs.

However I spotted that the main house has not got RCDs and am trying to do something about it while I am there.
In this case I would say I am officially protecting a distribution circuit (i.e. the tails) so am ok with 1s but in practice I am also trying to ensure all the final circuits have fault protection which would suggest 0.2s.

This is my dilemma. Taken in isolation perhaps I should use a non time delay to give the 0.2s on all circuits but if someone then wants to add another circuit with an RCBO they will have a discrimination problem.
 
perhaps I should just tell him it is a new CU with proper RCD protection or nothing and hope my previous comments about lack of protection scares him into accepting that :)
 
I have just done one of them on a farm, main incomer had 100ma rcd then several submains protected by a 30ma rcd, problem they had was when their was a trip, for some reason 9 times out of 10 the main rcd would go and they'd have to wander up to the barn to reset it, installed a time delay version and all is now hunky dory!
 

Reply to time delay rcds in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
347
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
956
Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
Replies
8
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Im suppling distribution circuits and want to use the largest possible RCD available to avoid nuisiance tripping (its for outdoor street furniture...
Replies
2
Views
896

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock