Discuss TN-S or TN-C-S From this photo in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hi,
I undertsand this to be a TN-S system as the earthing arrangement comes along the SWA metal sheath surround but the Ze i got is 0.19 which falls out side the regs of 0.8.
Chameleon Electrical - https://www.------------/Chameleonelectrical/photos/a.162578514404078/251251892203406/?type=3&theater

I have also read on here that if the earth is then connected to an earthing block as shown on picture, it then becomes a TN-C-S! which doesnt make sense as the earth is outside the sheath not inside on the neutral!

Which is it?
 
That appears to be a loop through TNS supply.

The earthing block to which you refer is the main earth terminal for the installation. This can be a separate entity, as it is in your photo, or the earth terminal bar in the consumer unit.

The main earth clearly comes off the sheath of the cable (this is what makes it TNS) into the main earth terminal. If it was TNCS, the earth block would be on the other side (the neutral side) of the service head, usually with the main earth leaving the service head on the same side.

As for the Ze... 0.8 is the maximum recommended I believe (i.e. if it's more, give the DNO a call). 0.19 is much lower and so it's a fine example of a good earth. No problem there.
 
0.19 is better than 0.80, so good there, however in answer to the question I would say it is TNS
 
deffo TN-S,but why is the isolator fed in at bottom instead of at top?
 
Looking at the photo I have come to the conclusion it is TN-S as if it was an old TN-S and converted to TN-C-S there would have to be a link between the neutral block and earth all I can see is a link between the sheaths and a earth link between the sheath of one cable and a earth block.
 
If you are unsure if its a TNS or a TNCS system by looking at it ( ie not sure if its been upgraded to TNCS ) You could do a simple continuity test between the neutral & earth at the mains switch to confirm this.

That won’t necessarily help as N and E are still linked at the substation for TNS so there is continuity between them in both systems.
Comparing the measured resistance may help, but it’s not guaranteed.
 
Hi,
I undertsand this to be a TN-S system as the earthing arrangement comes along the SWA metal sheath surround but the Ze i got is 0.19 which falls out side the regs of 0.8.
Chameleon Electrical - https://www.------------/Chameleonelectrical/photos/a.162578514404078/251251892203406/?type=3&theater

I have also read on here that if the earth is then connected to an earthing block as shown on picture, it then becomes a TN-C-S! which doesnt make sense as the earth is outside the sheath not inside on the neutral!

Which is it?
0.8 ohms is the typical value for TN-S, though some would say the ‘typical maximum’.
Anything below 0.8 ohms is acceptable, above would be a concern.

That earthing block does not look connected to the neutral.
If it is, then it is likely that the DNO have converted it to TN-C-S.

Not sure if that’s two supply cables, or a looped supply.
100A main fuse suggests a looped supply.

Although the supply may be TN-S, network upgrades may mean PME conditions may apply.
 

Reply to TN-S or TN-C-S From this photo in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K
I have just carried out an EICR at an old property and found this issue with the main earthing conductor. It has a TN-S system but the earthing...
Replies
32
Views
5K
On another thread there was chat about the N-E voltage to be expected, so I decided to measure my flat out of curiosity as it appears to be TN-S...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock