This is all really helpful stuff! Thanks guys (Although I resent them being referred to as Spuds! Haha) One question, perhaps a silly one. How are we supposed to ascertain the length of overhead or underground LV or HV network cables in order to complete the CRL risk assessment equation for Lightning strikes? I've phoned a mate at our local DNO and he doesn't think their maps would be available to mere Sparkies like what we is?
 
This is all really helpful stuff! Thanks guys (Although I resent them being referred to as Spuds! Haha) One question, perhaps a silly one. How are we supposed to ascertain the length of overhead or underground LV or HV network cables in order to complete the CRL risk assessment equation for Lightning strikes? I've phoned a mate at our local DNO and he doesn't think their maps would be available to mere Sparkies like what we is?

That scenario is covered in BS7671 and gives you a guide of I think 1000M. If you have to use the estimate distance in BS 7671 it is always going to direct you to install SPDs.
 
Didn't the bod who did the talk FOR the NICEIC (he's not NIC himself) say the financial cost was to be... either £1000 or £1500. If the risk of damage is over that in a domestic situation you have to fit a SPD?
 
Didn't the bod who did the talk FOR the NICEIC (he's not NIC himself) say the financial cost was to be... either £1000 or £1500. If the risk of damage is over that in a domestic situation you have to fit a SPD?
Don't know Richy, but I bet he was paid by the NICEIC.
 
Didn't the bod who did the talk FOR the NICEIC (he's not NIC himself) say the financial cost was to be... either £1000 or £1500. If the risk of damage is over that in a domestic situation you have to fit a SPD?
Thats gotta be most houses, considering TVs, set top boxes, gadgets on charge, kitchen appliances etc etc etc. Wonder who came up with that figure?
 
I'm happy that SPD have a place. But at home I've never had an incident that caused damage, nor do I know anyone that has had an incident. So I rank them right up there with the 6mm 32A cooker bonfires on Christmas Day, just saying. :rolleyes: .
 
Am I correct in thinking surge devices are single use only and once used should be replaced?
How often is mr and mrs homeowner going to check that little window for a colour change? Oh every time that test their RCD ofcourse:confused:
 

Reply to To Surge protect or not Surge protect that is the Question! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All. I am taking my 2396 written exam in December this year, therefore i am knee deep in practice papers. In case anyone else is in the...
Replies
8
Views
1K
Hi, I have recently had 18 solar panels (390W) fitted to my roof. The system is a GivEnergy. A Gen 1 Hybrid 5kW inverter (Gen2 version could not...
Replies
6
Views
3K
I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and...
Replies
7
Views
3K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
864

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock