Discuss Transformer in LED light fitting not working in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Meg464

-
Reaction score
1
Someone is asked me to have a look at a transformer in an LED fitting they have checked that it is not the fitting itself but they think it's definitely the Transformer inside it, does anyone have any thoughts or ideas about the best thing to do or how to fix the transformer or would it be best to just replace it and fit a new one?
Thanks in advance!
 
Check that there's a 230V supply to the light fitting first. If there is the problem will either be the transformer/driver or the LEDs themselves. In most cases it's the driver at fault.

Has it always been an LED fitting or was it a halogen fitting that's been converted to LED? If it's a conversion, it could be that the LEDs don't draw enough current for the existing transformer which may have a 20W minimum or similar.

If it looks like the driver/transformer at fault, you can buy replacements. They are not usually repairable.
 
Might be worth checking for a fuse, some of the fuse holders on transformers are molded and aren't always obvious.
 

Reply to Transformer in LED light fitting not working in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Great forum with lots of advice read and greatly received over the years! I have a question here that I am hopeful somebody here can...
Replies
16
Views
1K
Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
633
Good Morning, I've used this forum for advice many times but this is my first time posting so I hope that this community can help! We're...
Replies
5
Views
1K
Hi we are replacing light fittings in our home. Im confident with the fitting aspect, but have run into doubt in making the right choice of...
Replies
2
Views
520
I have halogen lights in my kitchen under the wall units, there are ten lights altogether bulbs are either 10 watt or 20 watt G4 bulbs ( not sure...
Replies
1
Views
761

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock