Discuss TT and RCD protection in the UK Electrical Forum area at ElectriciansForums.net

Yeah. The requirement for RCD protection has been replaced with an option for RCD protection or on OCPD. For an OCPD to be used the Zs must be 'permanently and reliably assured'.
 
411.5.2 -

'One or more of the following types of protective device shall be used, the former being preferred:

(i) An RCD
(ii) An overcurrent protective device.

NOTE 1: An appropriate overcurrent protective device may be used for fault protection provided a suitably low value of Zs is permanently and reliably assured.

NOTE 2: Where an RCD is used for fault protection the circuit should also incorporate an overcurrent protective device in accordance with Chapter 43.'
 
Yes, but the 17th had the same requirements. The 16th Edition mandated RCDs for fault protection as I recall, but the 17th definitely didn't.
 
Essex, you're always (or rather 99.9% of the time) going to need an RCD for TT as you'll never be able to meet the Zs values unless the Ra<1Ω which (unless you are Trev) is nigh impossible.

I'm pretty sure that reg you have given was in the 17th, so nothing new. Would be very interesting to know if anyone on here has ever been able to get an Ra low enough to forgo an RCD on a TT though?
 
Essex, you're always (or rather 99.9% of the time) going to need an RCD for TT as you'll never be able to meet the Zs values unless the Ra<1Ω which (unless you are Trev) is nigh impossible.

I'm pretty sure that reg you have given was in the 17th, so nothing new. Would be very interesting to know if anyone on here has ever been able to get an Ra low enough to forgo an RCD on a TT though?
Once got an RA of 6 ohms on a steel farm building by drilling and tapping a girder for the lug.Would have been ok for a B6 on a lighting cct I think.
Regards S
 
Essex, you're always (or rather 99.9% of the time) going to need an RCD for TT as you'll never be able to meet the Zs values unless the Ra<1Ω which (unless you are Trev) is nigh impossible.

I'm pretty sure that reg you have given was in the 17th, so nothing new. Would be very interesting to know if anyone on here has ever been able to get an Ra low enough to forgo an RCD on a TT though?

I would bed to differ. The last TT system we tested was 0.73 and that was only a single rod.

Although I do agree it is unlikely to be ever able to prove a permanently and reliable Zs on a TT system it does loosen the requirements a little and in this case a 500mA RCD would be more than enough.
 
I would bed to differ. The last TT system we tested was 0.73 and that was only a single rod.

Although I do agree it is unlikely to be ever able to prove a permanently and reliable Zs on a TT system it does loosen the requirements a little and in this case a 500mA RCD would be more than enough.


Think the installer may have hit an earthed source . Done loads of TT systems, to get an RA of 0.73 ohms with one electrode I’d need to see it to belive it and then see it again
 
Think the installer may have hit an earthed source . Done loads of TT systems, to get an RA of 0.73 ohms with one electrode I’d need to see it to belive it and then see it again
Had one the other week and it's been bone dry for a while...

IMG_1624.JPG
 
A few weeks ago managed to get 4 rods down (don't recall ever getting that far down before!), thought happy day's this will be nice and low. 60 ohms:(

Start of the year, same street, 2 rods down, 9 Ohms.
 

Reply to TT and RCD protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
377
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
735
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
795

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock