Hi doing an eicr on a tt system, plastic board, bonding ok! It is a split 16th edition board with 80amp 100m/amp main switch which has the lighting, smokes and boiler on. On the other side is a 63amp 30m/amp rcd protecting sockets, cooker and shower. The Ra is 28 ohms.

anyway my interpretation of the regs is that for the circuits protected only by the main switch rcd that this would still merit a C3 for not be protected to 30m/amp, would you guys agree? Cables buried in walls less than 50mm and not protected via anything!

thanks

craig
 
I see what you are saying but even if covered by a 30mA rcd the zs factor is still the same, so circuits protected by a 30m/A rcd would also be a code 2! Haha think I have just answered my own question, C3 it is then!
 
Interpretation of the Regs. is always a bit of a mine field.
For instance, generally there is no requirement for any circuit, other than those of a location containing a bath or shower to be provided with 30mA RCD protection.
In this particular instance, the requirement is to provide Additional protection for cables concealed in walls, one of the acceptable methods includes the provision of 30mA RCD protection.
 
I am not here to argue with you, i haven't seen the job. Does it comply with the requirements in place at the time it was first put into service, if so then you can only recommend C3 for improvements.

Just for info under current regs the usual set up for domestic TT would normally be 100mA RCD Main Switch protecting the whole board, and then 30mA RCD's for final circuits however you choose to configure it using RCD's for banks for MCB's or RCBO's etc. You have to have a maximum of 30mA for additional protection as this ensures that the voltage under fault conditions stays at or below 50V which is the safe touch voltage.

I use the word "Usual" lightly, there are other conditions that may change what i have written.

Cheers…………Howard
 
If it's a 100mA type-s up front then for the circuits not protected by the 30mA RCD then its a C2 as they won't meet required disconnection times and a C3 for circuits not having additional protection by 30mA RCD, if its a 100mA up front then it's just a C3 for any circuits that don't have additional protection by 30mA RCD.
 
If it's a 100mA type-s up front then for the circuits not protected by the 30mA RCD then its a C2 as they won't meet required disconnection times and a C3 for circuits not having additional protection by 30mA RCD, if its a 100mA up front then it's just a C3 for any circuits that don't have additional protection by 30mA RCD.

Always nice to be enlightened, Cheers.
 
As has already been stated, if the installation complied with (and still complies with) the Regulations in force at the time of design. Then there is no justification for a code C2, in this instance.
There is no requirement in the Regulations for existing installations to comply with current Regulations.
 
As has already been stated, if the installation complied with (and still complies with) the Regulations in force at the time of design. Then there is no justification for a code C2, in this instance.
There is no requirement in the Regulations for existing installations to comply with current Regulations.

Regardless of whatever regulations it was designed to if the overcurrent protective devices will not disconnect the circuit under fault conditions in the required time then it's a C2. An EICR is always carried out to current regulations.

Would you not code bare live cable not out of reach but in use that was designed to the first edition of the wiring regulations?
 
Thanks D Skelton, so basically if an upfront 100mA S type is the only rcd protection for the circuits, then your opinion is a C2 as disconnection times wont be met. But if it is a standard 100mA rcd then it is only a C3.
Not questioning you, but if you test the s type rcd and disconnection times are 20ms @ 1 time and 14ms @ 5 times, then surely disconnection times have been met. As BS7671 states a TT disconnection time of 0.2s for final circuits which equates to 200ms.

Anyone any input, i am always looking to learn?
 
Thanks D Skelton, so basically if an upfront 100mA S type is the only rcd protection for the circuits, then your opinion is a C2 as disconnection times wont be met. But if it is a standard 100mA rcd then it is only a C3.
Not questioning you, but if you test the s type rcd and disconnection times are 20ms @ 1 time and 14ms @ 5 times, then surely disconnection times have been met. As BS7671 states a TT disconnection time of 0.2s for final circuits which equates to 200ms.

Anyone any input, i am always looking to learn?

It is late and I have hit the booze , but firstly why would you x5 a 100mA , let alone an s type and secondly those look like 30mA times and a couple of hundred shy of where I would expect an s type to be ?

Like I say , late in the evening + fire water = possible wrong end of the stick on my part !:svengo:
 
Thanks D Skelton, so basically if an upfront 100mA S type is the only rcd protection for the circuits, then your opinion is a C2 as disconnection times wont be met. But if it is a standard 100mA rcd then it is only a C3.
Not questioning you, but if you test the s type rcd and disconnection times are 20ms @ 1 time and 14ms @ 5 times, then surely disconnection times have been met. As BS7671 states a TT disconnection time of 0.2s for final circuits which equates to 200ms.

Anyone any input, i am always looking to learn?

If those are your test results then it isn't a type-s up front. Also, as JD has said, you don't 5x a 100mA, 5x is only for 30mA or less when used as additional protection.
 
Those results were just for instance, I am just trying to get a point across and learn. I know you don't have to 5 x a 100mA rcd, which is not the point here, I am asking for advice and opinions on whether a C2 or C3 is applicable and in your opinions why?

Like I said if you test 100mA s type rcd @ 1 time and it is less than 200ms (0.2s) then surely disconnection times for a TT system have been met and circuits not protected to 30mA would thus warrant a C3?

Also if the 100mA rcd was not an s tpe would you C3 this, as needs Improving to an type?

Thanks for your replies!
 
Regardless of whatever regulations it was designed to if the overcurrent protective devices will not disconnect the circuit under fault conditions in the required time then it's a C2. An EICR is always carried out to current regulations.

Would you not code bare live cable not out of reach but in use that was designed to the first edition of the wiring regulations?

Oh dear.
To start with an EICR is a form, how you carry one is not something stipulated in the Regulations (current or otherwise).

A PIR conducted in accordance with BS7671 will identify (among other things) any departures from the requirements of the current Regulations which may give rise to danger.
Two codes are used for this purpose, Code C1 'Danger present' and C2 'Potentially dangerous'.
The code C3 is used to indicate that improvement is required in order for an installation to comply with the current Regulations, but that there is no danger.

Near the beginning of the current Regulations can be found this:
"Existing installations that have been installed in accordance with earlier editions of the Regulations may not comply with this edition in every respect. This does not necessarily mean that they unsafe for continued use or require upgrading".

To apply the code C2 (Potentially dangerous) in such circumstances would indicate that the earlier edition of the Regulations are unsafe.
I can assure you that the IET will never state that earlier editions of the Regulations are unsafe.

Use of the code C2 in such circumstances would not be in accordance with BS7671, and signing the declaration on the EICR would either constitute fraud or indicate a lack of knowledge.

I do not have my copy of the First edition to hand, but I doubt that uninsulated live conductors were allowed to be within reach.
 
Oh dear.
To start with an EICR is a form, how you carry one is not something stipulated in the Regulations (current or otherwise).

A PIR conducted in accordance with BS7671 will identify (among other things) any departures from the requirements of the current Regulations which may give rise to danger.
Two codes are used for this purpose, Code C1 'Danger present' and C2 'Potentially dangerous'.
The code C3 is used to indicate that improvement is required in order for an installation to comply with the current Regulations, but that there is no danger.

Near the beginning of the current Regulations can be found this:
"Existing installations that have been installed in accordance with earlier editions of the Regulations may not comply with this edition in every respect. This does not necessarily mean that they unsafe for continued use or require upgrading".

To apply the code C2 (Potentially dangerous) in such circumstances would indicate that the earlier edition of the Regulations are unsafe.
I can assure you that the IET will never state that earlier editions of the Regulations are unsafe.

Use of the code C2 in such circumstances would not be in accordance with BS7671, and signing the declaration on the EICR would either constitute fraud or indicate a lack of knowledge.

I do not have my copy of the First edition to hand, but I doubt that uninsulated live conductors were allowed to be within reach.

Well thank you Spin for that rather patronising lesson on how to conduct myself whilst inspecting and testing an electrical installation. It might help you to know that I'm well aware how to code something that is potentially dangerous!

I couldn't care less what previous regulations state, I am inspecting the installation to current regulations and a major part of that procedure means determining whether or not the installation complies with the requirements for ADS. An overcurrent protective device not disconnecting a circuit in the required time under fault conditions IS potentially dangerous, and saying so is not tantamount to fraud, nor does it indicate a lack of knowledge?!?!?!? What a load of twoddle!

To use the quote from the current regs; "This does not necessarily mean that they unsafe for continued use or require upgrading". There you have it fella. This means that it may not in all cases be unsafe, but in some cases it could be. That is what the use of the words 'does not necessarily' indicate. If the IET would never say that earlier editions of the regulations were 'unsafe', or at least 'less safe' than the current, there'd be no need for them to keep changing them would there?!


I do not have my copy of the First edition to hand, but I doubt that uninsulated live conductors were allowed to be within reach.

I have read it, and nowhere does it say that in all cases a bare live conductor must be insulated whether it is within reach or not.


Finally, I couldn't help but pick out this little gem! Talk about contradiction!
To start with an EICR is a form, how you carry one is not something stipulated in the Regulations (current or otherwise).

A PIR conducted in accordance with BS7671
 
Last edited:
Those results were just for instance, I am just trying to get a point across and learn. I know you don't have to 5 x a 100mA rcd, which is not the point here, I am asking for advice and opinions on whether a C2 or C3 is applicable and in your opinions why?

Ok, I didn't know that the results were hypothetical. Still, if they were hypothetical and you already knew that you don't need to 5x a 100mA RCD then why did you include a hypothetical result for a 5x test?

My advice for the codes that would apply depending on the circumstances is in post ten.

Like I said if you test 100mA s type rcd @ 1 time and it is less than 200ms (0.2s) then surely disconnection times for a TT system have been met and circuits not protected to 30mA would thus warrant a C3?

An s-type won't be less that 200ms as a non-adjustable type-s is built with this figure as a time delay. A type-s can never be used to provide fault protection on a circuit where 0.2s is the maximum permissable disconnection time.

Also if the 100mA rcd was not a type-s would you C3 this, as needs Improving to an type?

In this circumstance I'd C3 it only because there would be circuits protected by a 100mA RCD that have no additional protection by way of a 30mA RCD. With the Ra you stated in your OP the requirements for fault protection are met with the 100mA RCD therefore a C2 is not applicable.
 
New posts

Reply to TT eicr code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
297
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
So I'm getting various responses to this depending on how things are interpreted. Here's a scenario: Assume property is a tenanted property...
Replies
25
Views
2K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
Did a couple of inspections on 2 x 2 bed ground floor flood damaged flats today, only 4 circuits in each, bizarrely one socket circuit and 2...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock