Discuss TT eicr code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Regardless of whatever regulations it was designed to if the overcurrent protective devices will not disconnect the circuit under fault conditions in the required time then it's a C2. An EICR is always carried out to current regulations.
Would you not code bare live cable not out of reach but in use that was designed to the first edition of the wiring regulations?
Having just read the whole of this thread,I am going to take issue with Damien and support the veiw of Spinlondon
My own understanding is that an eicr is carried out to ascertain whether an installation is safe for continued use,it is not carried out to determine if it meets current regs, rather it is it is compared to current regs for the purpose of the report and any deviations can be coded with that in mind
In the example being discussed,a TT system with a time delay 100m/amp Rcd,it does not meet curent regs for the reasons that have been posted
If it does not meet the current regs,it is then determined if it meets the standards that were in force at the time of installation and in this case it does
Remembering why the eicr is carried out,to determine if it is safe for continued use
Now to take a view contrary to the above and code the installation as potentially dangerous C2
It means there are millions off UK households that have installations that were deemed perfectly safe at the time that are now being considered dangerous,the IET got it wrong,massive rectification is required throughout the land
I suspect that my own interpretation of why an eicr is carried out and what determines the compliance of the system and to what regs is the only correct conclusion
One exception to the 16th and prior I would C2, is the thermal cut-out on old immersion heaters, as that was a proven defect that could cause fatalities.
It was generally acknowledged (unwritten) that on an EICR you go back one or possibly two editions before other factors start creeping in which would out of necessity would start to require improvements due to the age and purpose of the install (rental etc.), or in other words the further back you go the case becomes more compelling to require to at least update parts of the install. (more C2 than C3)
This rules out the 1st edition of the regs in this context.
The 15th edition now starting to become borderline (VOELCBs etc.), and anything prior starting to become obsolete.
Are there millions of UK households on TT systems protected by a lone type-s RCD??? I've never come across one. I've come across plenty protected by a lone 100mA RCD though, in which case the requirements for fault protection (in most cases) will still be met even by todays standards.
The millons statement might just be a "slight" exagerationnevertheless,there are indeed many many many,TT systems both now and in the past that not only employ this set up but are indeed very numerous, even until today
I am very surprised that you have never come across one,your area of the country must be very different to my own,where there is a rich mixture of all sorts and these types were as numerous as any Tnc-s or Tns
I was fitting this type of install in 2006 and 2007 for the local council where I was working at the time, It was the defacto standard set-up for about 16 years, 1992 up to 2008.
Hi D, it boils down to many factors, ie. is it rental where the LA might want their own improvements, or is it private.
You cannot force people to upgrade, nor can you scaremonger, it is basically a technical RA, as I said it was 'tacitly' suggested but unwritten that maybe two editions back was far enough before other factors came into play.
Is it scaremongering to say that something is unsafe by today's standards? I don't really think so. If I were to carry out an installation on a TT system today and relied on a lone s-type to protect the entire installation my work would be unsafe. Surely the same standard applies to existing installations.
See edit above, even now S/Os without RCDs may be a C3 (15th ed) if not used for equipment outdoors (16th ed).
As I said it is basically a technical RA, your own personal preference has nothing to do with it, the situation as a whole needs to be taken into account.
Hi D,
what I was saying 16th ed TT wise, is that you can use 100mA upfront where No outdoor S/O are used, or a 100mA s-type upfront feeding a 30mA half of the board (S/Os) for discrimination purposes, or a 100mA (not TD) and 30mA split, if you look at the drawings I posted it shows this clearly.
In the 16th generally only S/Os and the shower were on the 30mA side.
I also think there is a mistake in the attached text where it says "shock protection" I think it should say Fault protection.
The 100mA providing fault protection, not additional protection as defined in the 17th, hence C3.
but if that s-type was compliant when installed, i 'd lean towards a C3. can't see it being OK pre 17th and now potentially dangerous.
Sorry, the 0.4 seconds in the 16th (table 41A TN disconnection times in that edition) only applied to S/Os supplying outdoor equipment, it did not apply to other fixed final circuits where a 5 seconds disconnection time was allowed.
Reply to TT eicr code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net