I've recently completed a part p defined scope course but all of our testing was on TNS or TNCS systems, in our house we have a TT system and in the OSG I can't find much information on the maximum earth fault loop impedence, just says that it is likely to be higher than their TN tables? I might ring the IEE helpline tomorrow.
What do you use for your maximum figures on TT systems?
 
The maximum "allowed" is 200 ohms, however you should endeavour to get below 100 ohms!

Fingers crossed you've got RCD's fitted.
 
with TT, as said prevoiusly, max. is 200ohms, but the lower the better. however, with TT, you need 30mA RCD /s or RCBOs on all ccts. max. Zs is entered at 1667ohms. as you will be relying on the rcd for fault protection.
 
yes all the circuits are protected by a 30mA RCD, it is an RCCB? We had a full re-wire by a NICEIC registered installer 10 years ago.
Can you clarify on the max zs being entered as 1667 ohms? I'm not sure what you mean here, if the max is still 200? Thanks for the quick response guys, made up.
What about rcd trip out times? are these different with a TT system? I read something in the on site guide about this but got a bit lost. Don't worry I done these tests tens of times in college and it is sinking in, I look forward to getting more familiar with the tests when I get a part p mft in a few weeks.
 
The 200 ohms figure is actually Ra not Zs.....in effect your Ze should be max 200 ohms and Zs on final circuits may be higher...ie Ra+ R1+R2.
On a TT ignore the max Zs figures in 7671 for overcurrent protective devices and use the max Zs for RCD's,(as it is the RCd which provides earth fault protection on a TT).....given in table 41.5.
The 200 ohms figure is to allow for soil conditions deteriorating and Ra increasing.....in practice a much higher Ra will still meet the requirements.....the 200 ohms is a rule of thumb recommendation,not a regulation.The 1667 figure is the maximum Zs where earth fault protection is by a 30ma rcd (table 41.5....and note2)

The disconnection time on a TT is 0.2s for final circuits not exceeding 32a,and 5s for distribution circuits and finals exceeding 32a .(table 41.1.....411.3.2.4)
 
Last edited by a moderator:
sorry, wasn't quite clear in my last post. max. Ze should be under 200. it's the max. Zs ( for each circuit ) that is 1667.
 
confused? you will be, welcome to our world lol.....

resistance between rod and main earth (sometimes called Ze or Ra) should be less than 200 ohms whereas all final circuits should have a max Zs figure (loop) of less than 1667 ohms.

pretty much what they said grrrrrrrrrrrr
 
as i don't understand binary , am i a 1-5 person or a 6-10?
 
That is great thanks, I'm clear now that the max Ra for a TT system is 200ohms and for Zs 1667 ohms. Are they both likely to be much higher or just the Ra?
Which page is the table on for RCD disconnection times for TT systems? I'm struggling to find it sorry.
 
Last edited by a moderator:
That is great thanks, I'm clear now that the max Ra for a TT system is 200ohms and for Zs 1667 ohms. Are they both likely to be much higher or just the Ra?
Which page is the table on for RCD disconnection times for TT systems? I'm struggling to find it sorry.

Disconnection time for TT installations are page 46 Table 41.1 in BS7671.
 

Reply to TT system - maximum earth fault loop impedence? in the Australia area at ElectriciansForums.net

Similar Threads

Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
Do you encounter many issues with homeowners experiencing "tingling" from electric showers in homes with a TT supply system? Reason I ask is...
Replies
5
Views
2K
I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system...
Replies
12
Views
3K
Maximum Earth Fault Loop Impedance for OverCurrent Device was calculated 230/(MCB Rating*5) * Rule of Thumb is that correct? And how are they...
Replies
5
Views
2K
Hi there, I’m just hoping someone could clear something up for me at all. I’m just working my way through some test questions and I’ve come across...
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock