An Electrical Danger Notice would be more appropriate than a Certificate though!
hum. You are going to need a very big pack if you take that approsch
Discuss TT system with No RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
An Electrical Danger Notice would be more appropriate than a Certificate though!
hum. You are going to need a very big pack if you take that approsch
My two pennith, would it not be the Zs that is to be considered?
Reg 411.3.2.4 TT system; each distribution circuit disconnection time not exceeding 1 sec.
Then reg 411.5.4 would give the calculation to give the maximum ZS when using a OCPD giving disconnection time of 1 sec;
Zs x Ia (less than or equal to) Uo x Cmin?
Ok stand corrected.Its a final circuit though. If disconnection is achieved by an OCPD and 411.3.1.2 is adhered to then the maximum disconnection times applicable to a TN system may be used if the circuit doesn't exceed 32A.