Does the conection of a cooker fall within the scope of BS7671?
The fact that you would issue an MWEIC, suggests that it does.
Does either the cooker or any cables used to make the connection require ADS?
If either do require ADS, then if it is not already there, it must be provided.
 
My two pennith, would it not be the Zs that is to be considered?

Reg 411.3.2.4 TT system; each distribution circuit disconnection time not exceeding 1 sec.

Then reg 411.5.4 would give the calculation to give the maximum ZS when using a OCPD giving disconnection time of 1 sec;

Zs x Ia (less than or equal to) Uo x Cmin?
 
My two pennith, would it not be the Zs that is to be considered?

Reg 411.3.2.4 TT system; each distribution circuit disconnection time not exceeding 1 sec.

Then reg 411.5.4 would give the calculation to give the maximum ZS when using a OCPD giving disconnection time of 1 sec;

Zs x Ia (less than or equal to) Uo x Cmin?

Its a final circuit though. If disconnection is achieved by an OCPD and 411.3.1.2 is adhered to then the maximum disconnection times applicable to a TN system may be used if the circuit doesn't exceed 32A.
 
Last edited:
Its a final circuit though. If disconnection is achieved by an OCPD and 411.3.1.2 is adhered to then the maximum disconnection times applicable to a TN system may be used if the circuit doesn't exceed 32A.
Ok stand corrected.

PS but does not reg 411.5.4 apply to calculate max Zs when using ocpd on TT?
 
Last edited:

Reply to TT system with No RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
610
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751
Evening all, I have a little conundrum I need to get resolved. I’ve moved an EV charger from a single phase board that was on a 40a breaker and...
Replies
9
Views
551

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock