Discuss Types of rcbos in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

To my recollection, the earth is a functional earth that provides a current path to operate the electronic disconnector inside the RCBO even if there is a break in the neutral. This also results in sub 1MOhm IR results if the trailing earth is not disconnected prior to meggering the circuit.
 
one assume that the flying earth lead is not required in the product standard but some manufacturers have assessed the level of risk of a lost neutral as being critical to the operation and addressed this. Other manufacturers have realised that if there is a lost neutral then there are far bigger problems than disconnecting an RCBO, which will have little effect, and have assessed the inconvenience of an additional cable outweighs the fractional advance that may provide a stability that is not required.
 
Last edited:
There are two different standards to which RCBO's can be manufactured, one require the earth and one does not.
Neither is more sensitive or in any way better than the other
 

Reply to Types of rcbos in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Replies
9
Views
1K
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
3K
Hello everyone, I would be happy to hear your opinion about wiring RCBO inside switchboboards, panels. Here I attached some example. We have 9...
Replies
3
Views
889
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
914
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
730

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock