Discuss Using 7 Core Armoured as Twin and Earth ? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
4
My daughter has some 7 core armoured cable running to her garage which looks to be 1m2 or possible 1.5m2. It carries a 2-way external light switch connection to switch on 2 external lights ( house and garage) from either the house or the garage, and there is also a single 13amp socket connected. I have told them to use the socket for a lead lamp in the garage only - ie no heaters, etc. There is no RCD from what I can see.

An electrician has suggested that if the switching was removed, the cables could be paired up to run a 13a supply and add an external PIR light, saving the need to replace the 7 Core with 3 Core Armoured ( it's >20m length).

This doesn't sound right to me but would make perfect sense if its within regs - any comments most welcome.
 
Your description is a little hard to fathom out, any possibility of drafting a sketch of the wiring, and / or a photograph of the connections, and possibly get hold of a different Electrician, preferably one who knows what he is talking about.
 
Assuming you no longer require the two way switching yes you can parallel the conductors. Depending on the existing protective device the existing set up may be okay not taking any volt drop issues into consideration.
 
There is not 1.0mm size in the regs, and I have looked at some manufacturers and the smallest they do is 1.5mm. So most prob your cable is 1.5mm
Nothing wrong with pairing up the cables in the 7 core cable, as I presume the electrician will test it before doing anything.
 
There is not 1.0mm size in the regs, and I have looked at some manufacturers and the smallest they do is 1.5mm. So most prob your cable is 1.5mm
Nothing wrong with pairing up the cables in the 7 core cable, as I presume the electrician will test it before doing anything.
Spoon like your post,and agree with you, but I don't like doubling up cores, it's not something I have personally ever done, and not something I would necessarily do, like you say nothing to stop you doing so, just me being an old fert I guess.
 
Spoon like your post,and agree with you, but I don't like doubling up cores, it's not something I have personally ever done, and not something I would necessarily do, like you say nothing to stop you doing so, just me being an old fert I guess.

We did have a contract that had 2 x 400mm XLPE/PVC/SWA/PVC cables going from the phase shift transformers to the dist cabinets..
 
We did have a contract that had 2 x 400mm XLPE/PVC/SWA/PVC cables going from the phase shift transformers to the dist cabinets..
That's a distribution service Spoon, bit of a step down from doubling up on final circuits, but I get your drift.
 
That's a distribution service Spoon, bit of a step down from doubling up on final circuits, but I get your drift.

Yeah, biggest I've designed. 3 x 3 phase transformers & 4 dist cabinets.

haha.... The principle is the same mate. It saves the OP getting a new cable installed, if the existing 7 core is fine.
 
We double up conductors on some jobs to get around voltage drop, often this is using hybrid cables containing copper and fibre.

In domestic I would make a note at source as to why the cables are doubled up, no doubt someone in the future might know no better and decide to remove a couple of the cores.
 
Makes no difference providing they are equal cross sectional area.
I know you don't need to point out the obvious Westy, as I said earlier, but I do take issue with doubling up conductors on final circuit conductors, as they are planned and more care is taken during installation, hence a safer install.
My issue is doubling up as a remedial action, I realise it's OK to do so, but just because it is safe to do so , doesn't mean I have to like it.
 
I know you don't need to point out the obvious Westy, as I said earlier, but I do take issue with doubling up conductors on final circuit conductors, as they are planned and more care is taken during installation, hence a safer install.
My issue is doubling up as a remedial action, I realise it's OK to do so, but just because it is safe to do so , doesn't mean I have to like it.
It is an existing cable so make use of what you have. The OP has asked is it okay, yes it is. Saying you don't like it is clouding the issue.
 
I know you don't need to point out the obvious Westy, as I said earlier, but I do take issue with doubling up conductors on final circuit conductors, as they are planned and more care is taken during installation, hence a safer install.
My issue is doubling up as a remedial action, I realise it's OK to do so, but just because it is safe to do so , doesn't mean I have to like it.
I think my post may be a bit misleading, Distribution doubling up is usually a planned install, which is monitored and planned, where as final circuit doubling is often done as an after thought, or as remedial action. This is what I was trying to put over.
 
It is an existing cable so make use of what you have. The OP has asked is it okay, yes it is. Saying you don't like it is clouding the issue.

I dont think any of @Pete999 posts have clouded the issue. Just that he dislikes the idea, unless its been designed that way.
 
Pete - will do - I was struggling to explain it in words !!

I'm back up there tomorrow, so I'll try and sketch it as much as I can, but I suspect the 7 core is connected to the house wiring, somehere under a tiled (suspended ) floor.
 
Obviously in this case they are equal cross sectional areas, but why must they be.

I can understand it would make design easier, but not sure of the specific reasoning.

Cheers
If they are the same csa the resistance is equal so the load is balanced across the two. Differing csa will result in an imbalance across the two.
 

Reply to Using 7 Core Armoured as Twin and Earth ? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Trying to find an armoured cable behind plasterboard and studding. It was used to supply power from the house but has been disconnected Can...
Replies
2
Views
437
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
458
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
212
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
748

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock