Discuss Very Strange RCD problem in the Australia area at ElectriciansForums.net

jibjob

-
Arms
Reaction score
17
Now this is a bit of a head sratcher. I've been called to a property where the RCD (used as main incomer) trips at exactly the same time every evening (7.50pm). Some work has been carried out recently at the property by another electrician. He installed new wiring via a 2 way stand alone C.U. also with a RCD as incomer fed from a Henley block which splits the supply between the 2 boards. The existing C.U. has just 3 circuits.

My initial thoughts were that something was coming on in the house at that time whether it be an o/s light, boiler, plug-in timer etc but all these possibilities have been iliminated. The RCD (30mA old style Steeple) failed the ramp test and also x1 & x5 tests so it'll have to be changed but not sure if failing these tests are significant anyway.

Iv'e done IR across all circuits, and got all the zero's across E-N with the lights cpc connected to the earth bar, all the nines with cpc disconnected. All other circuits checked out fine. Left cpc disconnected over night but still the RCD tripped at 7.50pm.

Western Power have been and had a look on their side but could find nothing unusual (I wasn't there, this was according to house owner).

Earthing is TT.

Customer insists there is nothing connected that would come on at the time stated, there's no immersion just a combi boiler that's not timed to come on, in fact at this time of year it's just used for instant hot water. Customer says that this problem began after the last electrcian finished but I'm not sure the two events are related.

Anybody got any ideas?
 
Frost free fridge freezer? They're designed to switch a heating element on each day to defrost any ice build up.

Possibly but I think they un-plugged it when the problem began so it wouldn't of been on load on one of the occasions when it tripped
 

Reply to Very Strange RCD problem in the Australia area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
346
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
863

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock