Discuss Views on Minor Works Certs in the UK Electrical Forum area at ElectriciansForums.net

Raptor0014

Esteemed
Reaction score
1,261
Morning all.

I was chatting with another spark the other day and he’s telling me I’m making excessive work for myself by issuing minor works certs for everything I do that isn’t covered with a EIC.

Eg if I change a socket I check everything first (Ze, Zs, PEFC, PSSC, R1+R2, RCD Trip times etc) firstly to see everything is in order and secondly to make sure it’s still in order once I’ve done the work.

I then issue a minor works cert to the customer along with the invoice.

He was saying that if I’m just replacing like for like then there’s no requirement as I’m not altering the circuit in anyway. I should only do a minor works when adding to a circuit.

I understand his point, but for me that seems wrong as I now have documented evidence that what I have done hasn’t altered the circuit in anyway.

So just wondering what others do and if I am indeed making excessive work for myself? 🤷🏼‍♂️
 
You do whatever you need to cover your backside. Is it making more work? Possibly, is it covering your backside yes.
Indeed.

To be honest I don’t see it as excessive. It might save me 10mins on site to skip the checks and maybe another 10mins tapping away on my iPad.

But just wondered what others views were on it.
 
If you always decide not to bother with the tests and cert, you will save 10min per job and it will all add up.
however you do run the risk of one day getting a call after the place burns down or other serious incident.

I would much prefer to be answering questions to the police or courts with a piece of paper in my hand backing up my claim that the circuit I worked on was safe when I left it.
much better than just having to say something along the lines of it all looked ok when I left it!!

edit,
although I have just posted this, I wrote it about half 11 this morning and forgot to press the post button!
 
For me it's not as simple as "I always do a MWC" or "I never do a MWC"
I do always test before and after and note the results, but if it's a single accessory change and
a) I'm already 2 hours late for a larger job
b) I need to get to the wholesaler before it closes
c) the customer has limited time
d) the customer is venting to excess about the contents of the Daily Mail
e) the house smells as if someone has been microwaving dead cats
f) my wife says I'm supposed to be somewhere else

I might decide not to.
 
I don't do this often (not commercial work, etc) but would not be happy changing a socket and not testing it afterwards, even if as an absolute minimum it is just a socket tester (polarity & CPC present) and the RCD trips OK (e.g. if unexpected request at friend's place).

Do what makes you feel safe/happy with the work but as above you could skip some tests before if it looks a recent and well-made installation.
 

Reply to Views on Minor Works Certs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
933
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
876
Hi everyone, I’m brand new to the site and hope everyone is doing well. My question is this: I have a 2365 level 2 diploma and have been doing...
Replies
6
Views
1K
Just to be clear… I am going to do the correct thing here and pay for the correct parts…. I just wanted to start the discussion. My particular...
Replies
6
Views
264
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
655

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock