Discuss Voltage at light fitting that is turned off in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

B

BillyTheSparks

Hello,

I need some advice, I have wired and fitted 2x down lights with 7w Kosnic LED lamps. These are switched from 3 positions. They are on a circuit suppling 13 other down lights all with LED lamps. (All the wiring is new as it's a renovated house, which I've wired).

Now testing the conductors of the cables with the megger all tests are fine and clear. When the circuit is energised the lights work as they should (I have done this sort of thing before!)

When the light switch is in the off position the lights go off, but then 1 down light starts to flash intermittently.

I have tested at the light fittings and I'm getting 74v with the switch in the off position???!!!???

Can anyone help me with this little set-up? I have been tugging my hair out today trying to figure it out!

It's not a loose neutral, as all neutrals are connected with Wago's (Helacons). And I have taken the light fittings out of the circuit.

I have also had all the switches off and connected the wires together with Wago's but still getting the same voltage.

I'm starting to think I'm going mad, but I know that happened along time ago!

Could it be induced voltage in the 3core between the switches? I have turned off all circuits apart from this one so I know that it's not coming from anywhere else.

If it is induced voltage can I loose it somewhere using something? I have been thinking of ferrite magnets? But I don't know that much about them.

Could it also be the lamps? Has anyone had anything sililar happen to them?

Sorry to go on but it helps to get it down on the screen.

Cheer
Billy
 
I'm not certain but I seem to recall someone on here saying the lamps have capacitors in them , so could be discharge?

I have led plinth lights and the misses sees them flash occasionally
 
induced voltage. this can be improved by fitting a snubber ( or more than 1). across the sw L and N on each group of LEDs.
 
I'm not certain but I seem to recall someone on here saying the lamps have capacitors in them , so could be discharge?

I have led plinth lights and the misses sees them flash occasionally

I also thought it could be a discharge, but not all of the down lights do this. Could it be because there is only two on this sw line?

Could it be the lamps? they're not the cheepest, but I have had problems with the Kosnic 5w dimmable range.
 
I also thought it could be a discharge, but not all of the down lights do this. Could it be because there is only two on this sw line?

Could it be the lamps? they're not the cheepest, but I have had problems with the Kosnic 5w dimmable range.

dont think its because you have two, have you checked the other fitting for any voltage?
 
Hi, What is a snubber and where do I get them from?
it's a resistor and/or a capacitor combination. there are various ones. it has been suggested that a 330K resistor across L and N terminals in the one of the fittings might do the trick. a bit of trial and error involved. have you tried measuring the voltage with an analogue meter. ?
 
well, nick's just suggested 1 Meg. that's the trial and error part. try 1 Meg., and if it's no improvement, try a lower value. ( not too low, of course ). the combined R/C snubbers may well give a better result.
 

Reply to Voltage at light fitting that is turned off in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all. Removed an ancient light fitting, replaced with a newer one, the light comes on but can't be turned off with the switch. It was working...
Replies
23
Views
703
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
649
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
624
Hi Just replaced a bathroom extractor fan. I didn't alter any wiring. Both old & new have live & switched live. Trouble is, once activated, the...
Replies
5
Views
332
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
453

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock