Do you have a dimmer on the lights? I fitted led's back when they were still very new and the dimmer actually lets a little voltage past and the lights never went all the way off. Could only be seen at night though but it was twinkling.
Hi Joe, no dimmers on this circuit or any circuits in the house for that matter. No electrical control gear anywhere either.
It is definitely a capacitance building up (if thats the right way to think about it) on the strappers. I have done all tests possible (R1+R2, R2/R1/RN, Meggered at 1000v between all conductors on the 2way intermediate strappers. Removed all LED lights from the circuit and Meggered the complete circuit again. Disconnected the earth bond to the gas/water to see if I was getting anything from those. Tested for voltage on the water pipework in the house (altough all plastic apart form airing cupboard).
I have litterally been over this with a fine tooth comb, and this is the only thing that it can be. I would like to resolve the issue of the capacitance but it is a no-no as the house is now finished and chasing walls is out of the question.
I even removed the strappers and common from the switches at both ends of the 2way, and connected one strapper (black) to the live, and then tested for voltage at the 2nd 2way switch. I was getting 105v on the common (brown) and 60v on the 2nd strapper (grey).
I then isolated the circuit, put it all back together, and put a 2K2 resistor between the switch live and neutral (at the switch) this stopped the 74v which I had at the fittings, the only problem was it glowed red hot when the switch was on and suppling the fittings. Obviously it can't withstand the 240v running constantly through it.
Could anyone give me a clue on working out the size of resistor that would be needed?
It needs to be able to allow the 74v through it to neutral, but not allow the 240v to do the same.
So would a high resistor i.e 1M or above do this?
God my brain is fried......Please help.....