It was implied that the DNO had done such a test but I did re-ask the question and so far no explicit answers have been given. I was trying to rule it out but agree that we can't yet do so. However we do have numerical answers for insulation resistance that include some strange failures.

yes, it was your post I was picking up on really.
As to IR readings, again - I agree it must be significant that there are so many low results. Even the cooker I would class as low for the type of circuit!

I don't suppose the house is on a flood plain is it?
 
Guess that's the end of that. We will never know what problem was found

I think we're getting to the bottom of it.
The new build, as it was then, was ruffed in by a sparks, through the metal stud work, without protective grommets. The cables have now worn through and the phase is making fortuitous contact with the metalwork. Give it a few more months and we'll have a S/C.

Now how many circuits have been affected so far?
Upstairs lighting
RFC

Looks like a bit of a rewire.
 
I'm mightily cynical about this whole business: You've conducting water in a plastic pipe, attached to a plastic trap, attached to a plastic shower tray or porcelain bowl, sat on a wooden floor which is pulling enough current from some chaffed cable in a stud wall somewhere meters away that's sufficient to produce a tingle yet doesn't upset an RCD......

OP - I apologise, genuinely, for being this cynical, but it's just all a little too improbable! However, I do also hold a belief in the scientific approach which states that in any given problem, when ALL other possibilities have been removed, whatever remains - however implausible - has to be the truth.
 
However, I do also hold a belief in the scientific approach which states that in any given problem, when ALL other possibilities have been removed, whatever remains - however implausible - has to be the truth.]

Lol, cyncical? I should coco .........

Picard: Come back! Make a difference!
Kirk: I take it the odds are against us and the situation’s grim.
Picard: You could say that.
Kirk: If Spock were here, he’d say that I was an irrational, illlogical human being for going on a mission like this... Sounds like fun!

He is !
 
Just going to be right out there and chuck an idea in, is it any water or is it hot water, maybe a cable in contact with a water pipe an when temp increases the insulation has broken down enough to give a small voltage, of course the longer this problem the higher the voltage (possibly) just thinking outside the box really as it's seems other than tearing the house apart
 
I had a very similar problem, which I did post up on here.
i had found some voltage inthe running water under the electric shower.
my testing concluded there was low IR on one lighting circuit, very long story short, I found the 28w 2d fitting was connected L-E, and although some supplementary bonding was present I doubled up in the old fashioned places, retested after, and it was gone, I suspect just doing the light repair would have solved it.
the IR readings were still fairly good, nearly 2M ohm, even with the light connected wrong
 
Yeah, come on purple - let us know. You've had loads of good advice. Daz
 
Is Purple really not going to let us know how it ended? I'd really like to know? Theres been almost 5000 views!! Come on Purple!!
 
Last edited:

Reply to Voltage in shower waste! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Hi, We are renting and have a electric shower downstairs (extension) - a 9.5kW Triton T80Z fast-fit electric shower as well as a combi boiler...
Replies
34
Views
4K
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
210
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
465
Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
439

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock