voltage reading on the nuetral

Discuss voltage reading on the nuetral in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
8
Hello all,

Been to my local campsite to fit a hairdryer in the toilet blocks. Before starting works i ran through a few basic checks as the installation is prettry old. I checked the voltage at the main switch at the board. I got a reading of 216v phase and 10v on the neutral. Has anyone got any suggesstions as to why i would have 10v on the neutral. The supply for the toilet block is a long run from the cutout so i am expecting so volt drop.
 
Hello all,

Been to my local campsite to fit a hairdryer in the toilet blocks. Before starting works i ran through a few basic checks as the installation is prettry old. I checked the voltage at the main switch at the board. I got a reading of 216v phase and 10v on the neutral. Has anyone got any suggesstions as to why i would have 10v on the neutral. The supply for the toilet block is a long run from the cutout so i am expecting so volt drop.

Load current in the N-wire produces voltdrop.
But 10V is on the high side.
 
Hello all,

Been to my local campsite to fit a hairdryer in the toilet blocks. Before starting works i ran through a few basic checks as the installation is prettry old. I checked the voltage at the main switch at the board. I got a reading of 216v phase and 10v on the neutral. Has anyone got any suggesstions as to why i would have 10v on the neutral. The supply for the toilet block is a long run from the cutout so i am expecting so volt drop.

A Hair Dryer not Hand Dryer ? It's been yonks since I camped they have Hair Dryers now things have moved on
 
Would this stop me from performing an rcd test and struggle to get a zs reading. What realistically could i do to improve this ?

NO. and

No. and

depends how much you want to spend?

to improve your Zs, ask the DNO to upgrade the supply and convert it to TN-C-S
Install bigger cables for your final circuit.
Install bigger cable for your earth cable.
 
as i see it, and i may be wrong, in a circuit under load, there is a certain volt drop. this VD is on the L and N, but the E is still at 0v. so there will be a small voltage differential between the N and E, relative to the VD of the circuit,
 
How many Kv do you get through a HT on a Quad bike coil ? I split a HT circuit other day while it was running I was dancing around like a crack head with St Vitus dance much to the amusement of my 19 year old kid..FK me it hurt
 
Didn't know Abu Hamza was a spark.:)

He's not...

500-by-500-abu-hanger-300x300.jpg
 
OK please explain the physics behind the drawing I don't get it

It's just 3 resistances in series, each one drops voltage across it.

Uo = Supply voltage
R1 = Resistance of Line conductor
Rn = Resistance of Neutral conductor
RL = Resistance of Load

Voltage across Line V1 = Uo * (R1/(R1+RL+R2))

Voltage across Load VL = Uo * (RL/(R1+RL+R2))

Voltage across Neutral Vn = Uo * (Rn/(R1+RL+R2))

V1 + VL + Vn = Uo
 
Last edited by a moderator:
How many Kv do you get through a HT on a Quad bike coil ? I split a HT circuit other day while it was running I was dancing around like a crack head with St Vitus dance much to the amusement of my 19 year old kid..FK me it hurt

HT from coils is in the region of 15kV.
 
I found this site whilst researching another matter, (Newbie), but isn't the case of the low phase voltage and apparently high neutral voltage part of the same argument about exporting PME?, induced voltage (no load) can increase earth voltage relative to true earth and thus is the distribution system earth at the same potential as the true earth at the toilet block. The use of a local earth rod will certainly draw down the earth-true earth potential (if one exists), this and and the volts drop (as previously explained) would assist the neutral 'drifting' to a higher level. I believe the solution is check the earthing and run a quick calc on voltsdrop based on max current draw.

Doing both should give you the comfort that the system is all ok, and if it's a rural site then the cable may simply be undersized. Besides, isn't the campfire for both these purposes! :)
 

Reply to voltage reading on the nuetral in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock