Discuss voltage reading on the nuetral in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
8
Hello all,

Been to my local campsite to fit a hairdryer in the toilet blocks. Before starting works i ran through a few basic checks as the installation is prettry old. I checked the voltage at the main switch at the board. I got a reading of 216v phase and 10v on the neutral. Has anyone got any suggesstions as to why i would have 10v on the neutral. The supply for the toilet block is a long run from the cutout so i am expecting so volt drop.
 
Hello all,

Been to my local campsite to fit a hairdryer in the toilet blocks. Before starting works i ran through a few basic checks as the installation is prettry old. I checked the voltage at the main switch at the board. I got a reading of 216v phase and 10v on the neutral. Has anyone got any suggesstions as to why i would have 10v on the neutral. The supply for the toilet block is a long run from the cutout so i am expecting so volt drop.

Load current in the N-wire produces voltdrop.
But 10V is on the high side.
 
Hello all,

Been to my local campsite to fit a hairdryer in the toilet blocks. Before starting works i ran through a few basic checks as the installation is prettry old. I checked the voltage at the main switch at the board. I got a reading of 216v phase and 10v on the neutral. Has anyone got any suggesstions as to why i would have 10v on the neutral. The supply for the toilet block is a long run from the cutout so i am expecting so volt drop.

A Hair Dryer not Hand Dryer ? It's been yonks since I camped they have Hair Dryers now things have moved on
 
Would this stop me from performing an rcd test and struggle to get a zs reading. What realistically could i do to improve this ?

NO. and

No. and

depends how much you want to spend?

to improve your Zs, ask the DNO to upgrade the supply and convert it to TN-C-S
Install bigger cables for your final circuit.
Install bigger cable for your earth cable.
 

Reply to voltage reading on the nuetral in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
1K
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
1K
Hello, my name is Kelvin. I'm a trainee hydraulic engineer in Indonesia. I apologize if this question has been answered before / if this question...
Replies
2
Views
1K
So earlier this year I obtained a large machine with a couple of 3 phase motors in it, and the rest single phase. I bought a VFD, correctly wired...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock