If a property is full of PVC push fit fittings on the copper plumbing and only about a meter and half underground before entering the house because before that it's PVC again, what is the bonding requirements?
 
Without seeing the full picture , if your incoming supply is metal and in contact with earth it should be bonded near the stopcock, if its plastic / copper combinations you will have to use your own judgment of the situation. If it is bringing an earth potential into the building it must be bonded.


Go to the IET site and search "Wiring Matters" There is an article about plastic /metal combinations , and bonding. Also the OSG covers it too.
 
Last edited:
Totally agree with Ruston, Dosent matter how small that section of copper is, it is allowing a potential to enter the building and must be bonded in my opinion.
 
Totally agree with Ruston, Dosent matter how small that section of copper is, it is allowing an earth potential to enter the building and must be bonded in my opinion.
 
Without seeing the full picture , if your incoming supply is metal and in contact with earth it should be bonded near the stopcock, if its plastic / copper combinations you will have to use your own judgment of the situation. If it is bringing an earth potential into the building it must be bonded.

Must bond at incoming (stopcock) because of short piece of copper incoming. But would be impossible to crossbond every short piece of copper to copper.
 
Must bond at incoming (stopcock) because of short piece of copper incoming. But would be impossible to crossbond every short piece of copper to copper.


Sounds like a lash up, why is the incomer copper , and why have they used plastic joins to the copper piping.

A few pics would be nice to get a full view of this. . See the edit to my last post for guidance. We can't see the installation so is hard to say what you need.to do.but if your incomer is metal it needs to be bonded.
 

Reply to Water bond? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
945
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock