Discuss Wattage or Amperage of Transformer in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
I have seen a transformer rated at 10,000 watts with input voltage of 110v and output voltage of 220v. Can input voltage of 110v and wattage of 100 watts produce the output of 10,000 watts?

What determines the amperage or wattage output of a transformer? The voltage input/output formula is always available but I've never seem formula to calculate the input/output wattage. Any help?
 
No, it doesn't - the transformer does not multiply output power like that. It will step the voltage up though. This will be determined by the ratio of turns on input side and output side. There will be some energy losses due to heat and so output power will always be less than input power.
 
leaving losses aside for a minute. the output watts will be same as input watts.so the amperage will be same ratio as the 2 voltages. half the volts and double the amps. and vice versa. obviously, the output wattage will be slightly less than the input, due to transformer losses, e.g heat loss.
 

Reply to Wattage or Amperage of Transformer in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, DIY’er here. I need a replacement transformer but can’t find the exact model required anywhere. It is Golden Power GP-SW120DC0700(UK)...
Replies
1
Views
692
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
A potentiometer has a wattage rating of 3 and voltage rating of 100 what would this mean electrically, and how could u transform 25w into 3 watts I'm
Replies
3
Views
632
Hello, my name is Kelvin. I'm a trainee hydraulic engineer in Indonesia. I apologize if this question has been answered before / if this question...
Replies
2
Views
1K
Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...
Replies
3
Views
544

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock