Discuss What cable size and breaker would I need for two extractor fans in a public toilet? 1.5mm 3 core and a 20amp rcbo? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Yes, just asking the questionare you a spark?
It seems rather basicYes, just asking the question
One with a current carrying capacity greater than or equal to the rating of the breaker, with low enough impedance to ensure disconnection times are met and voltage drop is not too high, and greater than or equal to the load, which in turn should be less than or equal to the rating of the breaker.What size cable for 2 extractor fans in a public toilet?
Technically correct but somewhat unhelpfulOne with a current carrying capacity greater than or equal to the rating of the breaker, with low enough impedance to ensure disconnection times are met and voltage drop is not too high, and greater than or equal to the load, which in turn should be less than or equal to the rating of the breaker.
Of a type suitable for the conditions where installed.
Be careful mate. This is a public environment where literally anyone can come into contact with this work, and your neck is on the line as the bloke that installed it.What size cable for 2 extractor fans in a public toilet?
Thanks mate, I was just asking as someone’s done it and debating if they had installed the correct cable?Be careful mate. This is a public environment where literally anyone can come into contact with this work, and your neck is on the line as the bloke that installed it.
In the nicest way possible, if you need to ask this you shouldn't put yourself in the firing line.
That wasn't very clear from the question!Thanks mate, I was just asking as someone’s done it and debating if they had installed the correct cable?
Most domestic fan manufacturers require a 3amp inline fuse for their extractors and its normal to have a three pole isolation switch, one assumes this is in a work environment, therefore industrial/commercial?Total circuit load in amps?
Method C.At the moment my only answer is that no installation method of 3 core flat PVC 1.5mm cable is rated for 20 amps.
Strictly speaking method C is 19.5 amps. But we won't haggle over 0.5 of an amp. In fact running a 1.5mm directly to the 2 fans is also perfectly safe on a 20amp rcbo. But is it conventional, good practice or advisable? NoMethod C.
Not according to 4D5Strictly speaking method C is 19.5 amps.
If the rcbo feeds the fans directly than they can be treated like any "End of line" appliance and overload protection omitted. Short circuit protection only required and the 20 amp RCBO covers thatI was wondering if there were FCU's by the fans and that overload protection was provided that way.
It would be oversized if the 1.5mm was connected to a circuit where the loading can't be controlled directly, like a socket circuit socketIt's likely the RCBO is oversized but can't be sure without knowing more about the fans who knows.
In principle that's not an issue. Both fans won't take more than an amp or 2.Well under the capacity of the cable and the rcbo. The issue is, is the cable going to be protected properly under overload and short circuit conditions. It is Interesting how unconventional situations (like the OP, s) force us to look at a situation that we all know is instinctively wrong but can't immediately explain why (talking about myself here). Then we end up "going back to the drawing board" and having to figure out again.. "Why is this wrong?". Good exercise though!!If the OP has a clamp meter it would be interesting to know the current draw with both fans on.
That's 3-core as in 3 phase conductors, not as in T&E.Is it not 17.5 amps for a 3 core or am I losing plot again?!
You are most definately not losing the plot. It's there in black and white (or purple and white). But I think the key is that that 3 core is referring to 3 "loaded" conductors, as in 3 phase, whereas the 3 core referred to by the OP is containing just 2 loaded conductors
Does it not say 19.5 amps in the table "Tim Howard" posted?Not according to 4D5
It does, but that's Table 4D2A, not 4D5Does it not say 19.5 amps in the table "Tim Howard" posted?
Thank you for talking that through. I was certainly thinking in terms of overload and fault protection. I get that overload protection could technically be omitted. If (as in the case of many fans) the manufacturer advises 3 amp protection it still doesn't sit right with me that that 60 amps could theoretically flow (B curve) before it shuts off.The issue is, is the cable going to be protected properly under overload and short circuit conditions. It is Interesting how unconventional situations (like the OP, s) force us to look at a situation that we all know is instinctively wrong but can't immediately explain why (talking about myself here). Then we end up "going back to the drawing board" and having to figure out again.. "Why is this wrong?". Good exercise though!!
My bad - trouble with using app, too easy to choose wrong table.It does, but that's Table 4D2A, not 4D5
Then I stand corrected. I was, nt aware you had different tables for calculating current capacity.It does, but that's Table 4D2A, not 4D5
There are different cable types, so there have to be different tables.Then I stand corrected. I was, nt aware you had different tables for calculating current capacity.
That's a valid point actually as technically all motors should have overload protection. But the wattage of a standard 4" fan is very low.Should it jam its internal impedence will prevent large currents from flowing and if they did the fan windings would likely burn out long before the supply cable would be troubled. In fact you will sometimes come across fans that have "stuck" and on being released they carry on working. High internal impedence prevents the from burning outIs there a remote possibility of more current being drawn if the if the fan jammed or the windings were damaged and it failed to properly start and just hummed I wonder. Probably unlikely and academic.
Interestingly 4D2A conforms exactly with the table we use here (ROI) for pvc insulated cablesThere are different cable types, so there have to be different tables.
Reply to What cable size and breaker would I need for two extractor fans in a public toilet? 1.5mm 3 core and a 20amp rcbo? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.