With a cavity wall running down between a two drive way each client would like led brick lights. Other than swa, which is not that flexible to work with in such a small space, looking for tips on what other type of cable would be acceptable to use which is also easier to work with and terminate with the nylon stuffing glands on the back of each light.
 
As above NYY-J is an obvious choice, much like SWA but without the armour.

Also pretty tough is the Flexishield stuff, but more expensive and not easily available by the metre.

If you want something very easy to wrangle then H07RN-F is an obvious choice. Reasonably tough and UV-resistant, but not so rodent-proof at Flexishield. However, you ought to use ferrules on the ends of fine stranded cables for most terminal types.
 
I'd like to see the cost comparisons with the Flexicon/singles and the NYY-J
With effort added in, any complete cable is going to be cheaper.

However, NYY-J has solid cores so is not that flexible at the ends. But if you can get "Tuff Sheath" cable (Doncaster Cables, think Yesss stock it) they are coarse stranded like conduit wire so a bit easier to wrangle.
 

Reply to What is the best cable to run down a garden cavity wall to feed led brick lights on each side other than swa in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

For various reasons out of my control, we have wound up in a situation where we have 1.5mm SWA cables buried in these pillars and exiting out of...
Replies
95
Views
7K
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K
We are in the process of renovating our house, and would like to setup led strip-lighting throughout. of the options, this seems most attractive...
Replies
4
Views
793
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
I have a slightly odd requirement that means I am wanting to route a 3 core 4mm SWA cable (14mm outside diameter) from outside through a cavity...
Replies
3
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top