Discuss When can an RCD be omitted from a domestic cable run in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

At any time.
There is currently no requirement to provide RCD protection for cables, other than those that make up a circuit for a location containing a bath or shower.
 
The standard regs regarding the external influence of impact apply.
These regs are not limited to domestic installations.
 
If not protected by earthed metal sheath trunking or conduit at less than 50mm RCD required then
Earthed metallic sheath, earthed trunking or conduit, mechanically protected, be part of a SELV or PELV circuit or run in a prescribed route and provided with RCD protection.

Similar rules apply if if the wall’s internal construction includes metallic parts.
 
Earthed metallic sheath, earthed trunking or conduit, mechanically protected, be part of a SELV or PELV circuit or run in a prescribed route and provided with RCD protection.

Similar rules apply if if the wall’s internal construction includes metallic parts.

For those of you who think there is a requirement for RCD protection, you should learn to read.
It’s an option.
If you choose that option, it’s your choice, no one is twisting your arm forcing you to make that choice.
Oh and once again, I’ll point out that RCD protection is not an option for cables concealed above ceilings and below floors.
 
Stair lift. Medical equipment.
Circuits of locations containing baths and showers, socket circuits in agricultural/horticultural installations.
Such circuits require RCD protection whether they use an earthed sheath, earthed trunking/conduit or have mechanical protection.
Though I’m not aware of a requirement to provide RCD protection for stair lifts (don’t get me started, they drive me up the wall).
 
critical equipment can be supplied non-RCD to avoid danger if tripped. bit like our freezers. no RCD = no defrosted steaks and chickens.
 
Never understood this option to omit it for a freezer circuit, if the rcd trips there is likely to be a fault with your appliance. Deal with it by getting a new freezer and while waiting for delivery, find a mop.
that may be true of the freezer is on it's own RCD/RCBO, but not if it's plugged into a circuit with other appliances/sockets/boiler etc.,etc.
 

Reply to When can an RCD be omitted from a domestic cable run in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
968
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
572
Hi, thanks for reading this. Ive been asked to look at a job where the DNO connection (single phase 80A TT) is a long run to the final circuits...
Replies
4
Views
286
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
795
Afternoon all. Was wondering, when cables are run underground using mole/tunneling methods, how do people get around the requirement to mark...
Replies
3
Views
386

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock