Hi Sir, I'm having a Megger MIT 1525 15KV insulation tester. During testing test voltage is not increasing more than 2KV. these is no physical damaged to the equipment. what could be the reason? pls advise.
thank you...
 
Is it connected to the test piece?

If so, when there is a low impedance it will limit the voltage as to deliver more would result in a large current, as it is limited typically to 6mA

So 2kV 6mA would be circ 0.3 Mohm

If it isn't connected to anything and still not producing voltage (and you have the right settings etc) then it's faulty.

Edit: forgot to say, does it beep when you start the test (ie burn mode rather than discharge mode)?
 
Last edited:

Reply to Why voltage is not increasing more than 2K in Megger MIT1525 Insulation tester? in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Replies
10
Views
4K
My cheap and cheerful voltage tester packed up just before Christmas, so need to replace it (It lasted longer than the more expensive one I had...
Replies
25
Views
4K
Hi lads, I have a Megger 1552. I didn't really use it in the last couple of years. I was planning to get more into testing again, so sent it for...
Replies
8
Views
1K
Hi all, My first post here, thought I'd see if it was possible to get some advice or tips... Basically, I had a large amount of block paving and...
Replies
80
Views
13K
Hi guys, I am new to the forum so be nice! I used to install solar PV systems back when the tariffs were still good, and I've never had to go...
Replies
5
Views
5K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock