Discuss Will any led 12v DC transformer be suitable for 12v DC Extractor fan in the UK Electrical Forum area at ElectriciansForums.net

Is that 3 threads now on your bathroom?

Although we can give DIY advice, a bathroom is classed as a “special location” and there are additional regulation concerning what can and can’t be fitted.

A 12v fan should have come with a transformer… some have a run on timer built in.
An LED normally comes with a driver, not a transformer, and are classed as constant current not constant voltage.

Not all fans in bathrooms actually need to be 12v, and mains 230v can be used, even directly above a bath, but need to be designed specifically for that location.
 
Blowing the air out of the bathroom) is there any other purpose for it?

Yes there are many other purposes, based on the information you gave it could have been anything from part of a vivarium to part of an industrial process.

I-Transformer will be located outside the bathroom

That doesn't help very much.
Most SELV extract fans come as a kit which includes a transformer or power supply as required.
 
Is that 3 threads now on your bathroom?

Although we can give DIY advice, a bathroom is classed as a “special location” and there are additional regulation concerning what can and can’t be fitted.

A 12v fan should have come with a transformer… some have a run on timer built in.
An LED normally comes with a driver, not a transformer, and are classed as constant current not constant voltage.

Not all fans in bathrooms actually need to be 12v, and mains 230v can be used, even directly above a bath, but need to be designed specifically for that location.
thank you, I know about special location, just want to make sure the job is done properly by low budget certified electrician. the fan is Svarna ip44 rating, 4w , it has 2 options 220V and 12v, but for 12v transformer is needed. I know that if above 2.25m the fan is fine at 220v . But just for extra safety I wanted to use 12v DC. There is now special requirments regarding transformer in the manual. Please advise a transformer if possible. I checked dedicated transformers for fans, those are all AC. Surely any transformer that gives 12v and 4w should do? But I only see the ones with plugs, not for permanent wiring. Thank you
 
Yes there are many other purposes, based on the information you gave it could have been anything from part of a vivarium to part of an industrial process.



That doesn't help very much.
Most SELV extract fans come as a kit which includes a transformer or power supply as required.
this one doesn't come with (separate) transformer, it has 2 options to run at 220v or 12v. there is no transformer accessory on their website. So for 12v DC option it needs a third party transformer/power supply. The only specifics manual says
"12VDC voltage must not exceed between 10 - 13,6VDC."
Lo-Carbon Svara | Vent-Axia - https://www.vent-axia.com/range/lo-carbon-svara or Vent-Axia 100mm Svara Lo-Carbon App Controllable Extractor Fan Timer | Toolstation - https://www.toolstation.com/vent-axia-100mm-svara-lo-carbon-app-controllable-extractor-fan/p29639
 
thank you, I know about special location, just want to make sure the job is done properly by low budget certified electrician. the fan is Svarna ip44 rating, 4w , it has 2 options 220V and 12v, but for 12v transformer is needed. I know that if above 2.25m the fan is fine at 220v . But just for extra safety I wanted to use 12v DC. There is now special requirments regarding transformer in the manual. Please advise a transformer if possible. I checked dedicated transformers for fans, those are all AC. Surely any transformer that gives 12v and 4w should do? But I only see the ones with plugs, not for permanent wiring. Thank you

Can you not buy the matching transformer for the fan? I would go with manufacturer's recommendations rather than trying to find alternative type.

What is the model number of this fan?
 
Can you not buy the matching transformer for the fan? I would go with manufacturer's recommendations rather than trying to find alternative type.

What is the model number of this fan?
this one doesn't come with (separate) transformer, it has 2 options to run at 220v or 12v. there is no transformer accessory on their website. So for 12v DC option it needs a third party transformer/power supply. The only specifics manual says
"12VDC voltage must not exceed between 10 - 13,6VDC."
Lo-Carbon Svara | Vent-Axia - https://www.vent-axia.com/range/lo-carbon-svara or Vent-Axia 100mm Svara Lo-Carbon App Controllable Extractor Fan Timer | Toolstation - https://www.toolstation.com/vent-axia-100mm-svara-lo-carbon-app-controllable-extractor-fan/p29639
 
A 230v fan fan be used provided it is suitable for the location. Does your low budget electrician not know this.
 
this one doesn't come with (separate) transformer, it has 2 options to run at 220v or 12v. there is no transformer accessory on their website. So for 12v DC option it needs a third party transformer/power supply. The only specifics manual says
"12VDC voltage must not exceed between 10 - 13,6VDC."
Lo-Carbon Svara | Vent-Axia - https://www.vent-axia.com/range/lo-carbon-svara or Vent-Axia 100mm Svara Lo-Carbon App Controllable Extractor Fan Timer | Toolstation - https://www.toolstation.com/vent-axia-100mm-svara-lo-carbon-app-controllable-extractor-fan/p29639

It looks like any regulated 12V DC power supply can be used providing it can provide 4 Watts and is suited to running with such a low loading.

But as above, it is also suitable when fed with 230V

And avoid cheap contractors - there is usually a reason they are cheap!
 
A 230v fan fan be used provided it is suitable for the location. Does your low budget electrician not know this.
sure, but can we have 12v for extra safety of is it unreasonable to ask? Everybody knows above bath tub at 2.25m (zone 2) it is ok to have 220v with IP44, But still:) 12v is safer
 
It looks like any regulated 12V DC power supply can be used providing it can provide 4 Watts and is suited to running with such a low loading.

But as above, it is also suitable when fed with 230V

And avoid cheap contractors - there is usually a reason they are cheap!
I wouldn't be here if I could afford those
 
sure, but can we have 12v for extra safety of is it unreasonable to ask? Everybody knows above bath tub at 2.25m (zone 2) it is ok to have 220v with IP44, But still:) 12v is safer

Yes no problem at all. At least you are weighing up the options.
 
Looks like everybody is voting for 220v and giving up on advising 12v DC transformer because it is not common and not showing up in google:) I wonder what were the manufacturer thinking by adding 12v DC options since there is no suitable PS on the market. I will email them just out of curiosity.
 
Looks like everybody is voting for 220v and giving up on advising 12v DC transformer because it is not common and not showing up in google:) I wonder what were the manufacturer thinking by adding 12v DC options since there is no suitable PS on the market. I will email them just out of curiosity.

I advised about a power supply in post #13
 

Reply to Will any led 12v DC transformer be suitable for 12v DC Extractor fan in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi folks I've just identified as cause of lighting circuit tripping in consumer unit a low volts ceiling light with laride transformer taking in...
Replies
7
Views
285
Hello, I'm swapping my extractor fan in the UK and I have bought a Turkish extractor fan stupidly and the connections you can see in the picture...
Replies
1
Views
386
Hi, my niece lives in a flat and has a bathroom without a window. There is an extractor fan which packed up and an electrician installed a new one...
Replies
4
Views
800
1964 house old style wiring Need to wire a extractor fan up Is it possible to wire the extractor fan to report switch there's 2 red wires in the...
Replies
14
Views
963
Evening all, Got a vent axia TX6 6” fan I need to replace. A like for like replacement is around £500, client is asking for a cheaper option...
Replies
8
Views
423

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock