i have been told the cable running inbetween two 50amp fuses should be 16mm i cant fathom this as a 6mm swa cable is rated to 62 amps, am i missing something here?
thankyou for your time
 

Attachments

  • C150 1-vaihe.pdf
    35.2 KB · Views: 153
i have been told the cable running inbetween two 50amp fuses should be 16mm i cant fathom this as a 6mm swa cable is rated to 62 amps, am i missing something here?
thankyou for your time
Hi - reading Table 4D4A for multicore armoured the biggest number shown is 53A. So my internet design thought is 10 might be ok, but 16 will be :) .
I am having a dense moment trying to understand the drawing though - it looks a bit like a fused neutral (?) or is that another phase? (on the LHS labelled C)
 
It's 3-phase heater bank paralleled up for single-phase. It is intended for operation on either 230V single-phase L-N, or 230V delta-derived single-phase where both wires are lines and both need fusing. This was a common system in mainland Europe that we never used in the UK.
 
If there was three phase supply available and someone who knows what they were doing on that job, you could reduce your conductor sizes considerably.

Assuming there is neither, if you have been told to run 16mm then run 16mm. 10mm could be fine but only under certain conditions. As already said this may have been specified following design calcs. Ze, Rating factors (ambient temp , grouping, thermal insulation etc) & cable length will all have a bearing on cable selection. It is not just simple current carrying capacity of cable clipped direct each time. If you can't calc it then run what you have been specified to.
 
thankyou for all your quick replies. im not a spark i just wanted a second opinion as this is the 3rd wiring diagram the company has sent me and the other 2 had errors on so before i payed someone to come in and do the work i wanted to be sure it was correct, it is a sauna oven with a conversion from single phase to 3 phase, again thankyou all very much at putting my mind at ease
 

Reply to wiring diagram just does not seem right in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just looking at my boiler wiring out of interest, and just wondering if it's wired correctly. So perma lives, neutrals and earths in the right...
Replies
65
Views
5K
Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
840
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
771
Hello I have some decking lights which to be fair, have been nothing but pain in the bottom since they were installed. Moisture in the lens lamps...
Replies
10
Views
2K
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock