Discuss Wiring help for Meross thermostat in the DIY Electrical Advice area at ElectriciansForums.net

KimbyK

DIY
Reaction score
0
I currently have a Myson thermostat that is no longer working. I have a Meross thermostat to replace it. I have attached photos of the current wiring and of the new thermostat. Could anyone advise on where the wires would go into the new thermostat?1000014992.jpg1000014991.png1000014994.png
 
The Meross thermostat requires a 240V mains supply, but your original Myson did not, so there is probably no mains supply in the wall there. There does seem to to be a spare wire but you would need to safely do some detective work to find out where that goes.

The simple way of resolving this would be to get a replacement mechanical thermostat,
or a battery powered one:

With that you would just put the two wires currently in the block at the top of the Myson into the 'COM' and 'NO' terminals of the new one.
 
Last edited:

Reply to Wiring help for Meross thermostat in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I’m looking to install 3 meross smart switches for 3 lights: entrance switch: only 1 gang but 3 way switch bedroom switch: 2 gang (1 is 1...
Replies
9
Views
362
Hi - we have an inline heater for a vent system that appears to always be on. I believe the electrician may have wired it incorrectly with only a...
Replies
3
Views
688
Hi all looking for some helpful advice I'm an Aussie so go easy on me, I have a good mechanical engineering head but first time plumbing and...
Replies
32
Views
2K
Hi everyone just looking for some advice before buying stuff not planning on carrying out this work myself will get someone who knows what their...
Replies
2
Views
333
Hi All I have been asked to supply a minor works certificate on a smart thermostat upgrade. Would I just test the dedicated circuit from the CU...
Replies
3
Views
281

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock